1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

arc gap discontinuity in CSA Z462 Standard D.8?

Discussion in 'CSA Z462 Workplace Electrical Safety' started by arcad, Oct 28, 2009.

  1. arcad New Member

    I have a question regarding arcing gap discontinuity in CSA Z462 D.8 derived from CSA Z462 tables D.6 and D.7. For visualization purposes, check a plot displaying arc gap as a function of system voltage - all according to tables D.6 and D.7 from CSA Z462, or tables 410-1 and 410-2 from the NESC standard.

    [IMG]

    The jump at 46kV point is most obvious and alarming. The problem with the 10kV/in number and arc gap calculated based on it is that it is used in calculation the distance from the arc to the worker, namely CSA Z462 Table D.7 Note 2 states the distance from the arc to the worker is calculated using the minimum approach distance from Table 441-2 of IEEE C2 and subtracting two times the assumed arc gap.

    Any comments?

    Sincerely, M. Furtak, C.E.T.
    www.arcadvisor.com
  2. Vincent B. Well-Known Member

    The minimum approach distance from Table 441-2 of IEEE C2 for 46.1 kV (3'-2'') is a lot longer than the 15 inches used for Table D.6 of CSA Z462-08.
    So a few inches more or less (from the substraction of 2 times the arc length taken as a flashover at 10 kV/in) won't change much in the end.

    Compare the jump from 78.7 cal/cm^2/s for 20 kA at 46 kV in Table D.6 to 12.4 cal/cm^2/s for 20 kA at 46.1 kV in Table D.7. That's because the distance from arc to worker is much longer, so less energy radiates to him.

    Also, this discussion should not be targeted at CSA Z462, but at IEEE C2 (where the values in Tables D.6 and D.7 come from, specifically Tables 410-1 and 410-2 in IEEE C2).
  3. arcad New Member

    "So a few inches more or less (from the substraction of 2 times the arc length taken as a flashover at 10 kV/in) won't change much in the end." [ quoted ]

    I've done some analysis ( see below ) and I think it does change a lot in the end.

    46kV working distance = 15in.. Gap is equal to 9in. ( from Table D.6 Note 2 )

    46.1kV working distance = min approach distance - 2 x gap ( from Table D.7 Note 2 ).

    Now, if gap was assumed to be equal to 2.7in. at 46.1kV ( as per Table D.7 Note 2 ) than 46.1kV working distance would be equal to approx 33in. = 38in - 2 x 2.7in. I agree the jump from 78.7 cal/cm^2/s for 20 kA at 46 kV in Table D.6 to 12.4 cal/cm^2/s for 20 kA at 46.1 kV in Table D.7 could probably be justified by larger ( twice as much ) working distance. Even in such case more than 6 times ( 78.7 / 12.4 ) heat flux reduction is quite profound and hard to believe.

    Now the logic dictates that the 46.1kV + gap should not be less than 46kV gap ( 9in.). Assuming at least 9 inch gap in 46.1kV system, than according to Table D.7 Note 2 the working distance would be equal to 20in. = 38in - 2 x 9in. that implies 78.7 / 12.4 = 6+ times heat flux reduction by moving just 5 in. = 20in. - 15in. further away from the arc ?

    I've put the numbers above together to make easier to visualize the problem I envision with the CSA Z462 section D.8

    [IMG]

    Comments?

    Sincerely, M. Furtak, C.E.T.
    www.arcadvisor.com
  4. Terry Becker Member

    FYI Annex D in CSA Z462 came from NFPA 70E. The CSA Z462 Technical Committee did not create any of this information.

    Regards;
    Terrry Becker, P.Eng.
    Owner
    ESPS Electrical Safety Program Solutions INC.
  5. arcad New Member

    do you mean you agree there is a problem with arc gap discontinuity in CSA Z462 and NFPA 70E?

    - Michael Furtak
    www.arcadvisor.com
  6. elihuiv Well-Known Member

    Arc Calculation Issues including arc gap

    There is definitely a problem.

    All the data in Z462 and 70E comes from two early papers.

    1. Ralph Lee's paper
    2. Dick Doughty's paper. Tom Neal, Dan Doan and Dick Doughty did some studies of arc flash in boxes. They did this paper a few times with refinements and we all did it together with some of my PPE research. This was the beginnings of IEEE 1584 but IEEE only spent about $60K on research on the early 1584 and at 15kV there is NO data. It all reverts back to the Ralph Lee equation which is TOTALLY theoretical. If you want something in medium voltage, use ArcPro. Most of those on the 1584 committee are industrially focused. I started in utilities and only ArcPro gives realistic energies with gaps in medium voltage. ArcPro was designed for T&D for Ontario Hydro. I have NO commercial interest in ArcPro. I do most of the arc testing at Kinectrics.

    IEEE 1584 has issues in medium voltage which are unlikely to be fixed because the focus of the committee is indistrial. EPRI has done a lot of research and starting more on longer gap arcs. This is being done at Kinectrics. The EPRI committee is focused on the medium voltage systems since the arc flash calculations are overkill when using the Ralph Lee equation. If you look at that equation, arc flash is DIRECTLY proportional to voltage. This is not true. If you don't work medium voltage hot, these calcs don't matter much but they matter to utilities. We use ArcPro with multipliers on medium voltage IF a customer must work it hot.