    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Current Limiting Breakers

Discussion in 'General Discussion' started by haze10, Feb 1, 2008.

  1. haze10 Well-Known Member

    How do you deal with Current Limiting Breakers?

    Say you are feeding a remote panel from a Fused Switch Disconnect. You have 200A Class R Current Limiting Fuses upstream of the panel. You calculate bolted fault to the panel and you get 16KA. You calculate Arcing Current at 11KA. But the fuse has a maximum let through current of 8KA. It would seem to me that since you know Arcing Current is greater than Let Through that the fuse will clear in less than 1/2 cycle and that the max let through would be 8KA. So for Incident Energy I would use the 8KA@1/2cycle. Is this correct?

    If the arcing current was less than the let through, I would then use the clearing time based upon the fuse curve for that arcing current value.

    Point I am trying to make here is that current at arc can never exceed let through current of the fuse.

    IS this logic correct?
  2. haze10 Well-Known Member

    Sorry, I was thinking Fuses but typed breakers. Thread is in reference to current limiting fuses. Although I guess it would apply for breakers that incorporate current limiting fuses.
  3. brainfiller Administrator

    Current Limitation

    Haze,
    You have the right idea but there are a few different formulas to use. The current limiting devices can reduce the short circuit current and arc flash energy. That is a major advantage the fuse manufacturers promote. There are some current limiting fuse formulas in IEEE 1584 which are also copied in the Annex of NFPA 70E that are used for RK1 and Class L fuses. You input the bolted fault current and the formulas predict the incident energy. You might also contact the fuse manufacturer for other classes of fuses.
  4. WDeanN Well-Known Member

    I must be pretty dense, because it wasn't until this point that I really realized the reason behind the other set of equations for current limiting devices. (The lower let through current.)
    I think they should have clearified this in the 1584 report, as well as perhaps giving the equations the same or similar format to the regular equations.
  5. brainfiller Administrator

    WDN - Yep just when you thought it was safe.. more forumulas! Guess we are all trying to figure this stuff out together. Can't wait to see what the next forumulas look like after the latest round of tests. I'll be meeting with the 1584 committee in a few weeks and if any new info shows up, I'll post it here.