1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

240/480V 1phase

Discussion in 'General Discussion' started by ronlow00, Oct 8, 2009.

  1. ronlow00 New Member

    Anyone figure out how to simulate this in EasyPower or how to calculate the hazards for this type of system?
  2. THE CABLE GUY Well-Known Member

    I have talked to ESA about this. As of now there is no AF calculations for single phase voltages that they utilize.

    You have a couple of choices.
    Click on the bus properties open the Arc FLash tab, 1. You can exclude the calculation until proper data creates a software upgrade to include single phase faults. 2. You can reference the upstream protective device and put in a simulated fault clearing time say 0.3sec. 3. You can enter the cal's/cm2 as a value you have calculated or your plans say to use for such cases as a default.
  3. THE CABLE GUY Well-Known Member

    I seen were Zog posted this comment about SKM and single phase modeling.

    Zog says, "You need to purchase the single phase module from SKM."
  4. amohammed New Member

    SKM does not calculate arc flash incident energy for the single phase system either. The single phase module they have is good for load flow studies and short circuit studies.
    A conservative approach to modeling the single phase system is to model it as a 3-phase system. Your software can then use the 1584 equations to provide you the desired results.

    There are couple of threads in this forum which discuss more on this subject.

    Regards.
  5. WDeanN Well-Known Member

    I haven't seen it, but the latest advertisement from ETAP is that they perform single phase arc flash studies.
    I would like to know what there calculation is based on.