1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

ppe

Discussion in 'Personal Protective Equipment (PPE)' started by PUCKMAN, Oct 8, 2009.

  1. PUCKMAN Member

    We have a 4000 amp 480 switch gear at our service and we lose power from utiliy from time to time. my question is can a quilified person reset or test a breaker and a bu generator without ppe? In the plant we have a hrc of 2* i am not sure about the switchgear rooms hrc. i would think it might be higher , we don,t rack cb in switchgear. but we do replace buckets and i don,t believe it is a hrc 2*
  2. PPE pertains primarily to energized work. If your qualified worker is exposed to energized parts within the Arc Flash Boundary, as determined from an arc flash study, he needs to be suited up in a PPE level equal to or greater than the incident energy level of the equipment. Using NFPA table 130.7(C)(9), operating (resetting) a circuit breaker with the covers on requires PPE level 0. Voltage testing requires 2*.
  3. Vincent B. Well-Known Member

    As long as the maximum available fault current is 35 kA and the maximum fault-clearing time is 0,5 s. Outside those ranges, you need to calculate the IE.
  4. Zog Well-Known Member

    The live parts do not need to be exposed for arc flash PPE to be required.

    I would not recommend using the tables for the OP here, with 4000A switchgear I highly doubt they are able to use the tables.
  5. PUCKMAN Member

    Thanks to everyone for the responses. I spoke to the safety guy about the size of our service 480, 4000 amp, that it might be out side the limits for using the tables for hrc uses, they set our electric safety plan according to the tables in 70e book and want us to follow it. Thats good but told them in the long term it might be a problem. Since it came down from his boss Idon,t see much changing. I don't know much of the rules for the limits to relate them to the safety people to understand.

    Great info from you guys, thanks again.