1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Labeling PDUs by Liebert

Discussion in 'Arc Flash Labels' started by amohammed, Oct 6, 2009.

  1. amohammed New Member

    Hi

    Has anyone dealt with labeling Liebert's Power Distribution Unit (PDUs) or FPCs? These units typically have a 480V main input circuit breaker, a 480/208V transformer and 2 to 4 208V panels (fed from the transformer), all in one cabinet. My dilemma is, do you label all the power panels (each of which has 208V main breaker) by one label indicating the incident energy on the line side of the main breakers or by printing one label for each panel indicating incident energy of the load side of 208V main breaker? I guess I would like to know your approach on labeling this kind of equipment which has multiple incident energies across it.

    Following is the link where you will find more info on Liebert's PDU (called PPC now): http://www.liebert.com/product_pages/ProductDocumentation.aspx?id=79&hz=60

    Thank you for your time.
  2. WDeanN Well-Known Member

    This is my vote, assuming, of course, that the transformer is >125kVA, and that it is all contained in one cabinet. By labeling the line side of the mains, you are looking at the worst case scenario.
    I would provide a label for the 480V section, regardless of the 208Y/120V section.
  3. Vincent B. Well-Known Member

    Also, verify the IE at the secondary of the transformer (assumed >=125 kVA), when the upstream protection device is on the primary of the transformer.
    The longer FCT associated with the lower arc current may give a higher IE.

    I just calculated that for kicks for a 125 kVA transfo, and I get a IA (on secondary) which, when reflected at the primary, is about 12 times the nominal current (depending on the upstream fault capacity), just at the border of the INST region (from the TCC of a CB I had close). 85% of that IA can probably push you into the short-term region (depending on your actual primary protection device), where the IE can go up because of time.

    My final word: evaluate all different possibilities before putting the label, and use the worst one.