1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Transformer grounding

Discussion in 'System Modeling and Calculations' started by amohammed, Sep 28, 2009.

  1. amohammed New Member

    I am working on an arcflash study for an aircraft manufacturing facility which involves quite a few 4160 - 2400 /480 - 277V Y-Y (solidly grounded secondary) connected transformers. Since all these transformers are inside an enclosure (which is locked), it is hard to tell if these windings are grounded or not, unless the facility owner or the drawings indicate it.
    Although my perception tells me the primary Y connection should be grounded as well, is there any possibility of not grounding the primary? Obviously, I will bring this issue up with the client but I doubt if they will have an answer for every transformer. In general, what is the grounding philosophy for intermediate systems (For example: commercial facilities that has lots of fans, chillers, computer loads etc..)?

    Thank you.
  2. acobb Well-Known Member

    If it is a Y-Y with grounded secondary, then the primary should also be grounded. If they are padmounts then many have the primary and secondary neutrals tied internally. Depends on the design.

    Alan