1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

HP of hermetic refrigerant motor-compressors

Discussion in 'System Modeling and Calculations' started by FEC2, Sep 24, 2009.

  1. FEC2 New Member

    The typical chiller with hermetic refrigerant motor-compressors will list rated load current (RLA) and/or locked rotor current. Does anyone have a better method for determining a motor HP than thru NEC tables 430.250 and 430.251(B) which are for standard induction motors?
  2. JJH Member

    Great question. I also use the tables to estimate the horsepower. Maybe others have a better method?
  3. Vincent B. Well-Known Member

    (My question is probably a stupid one...)
    Why do you want the HP of your motor if you already have the RLA? For electrical modeling purposes, usually you do the opposite (from HP to RLA/LRC if only the HP is known).

    Now, if you are on the mechanical side of things, then knowing the HP can make some sense (or if you need the torque).
  4. FEC2 New Member

    When using the SKM software, the default input is motor HP. The software then models the decaying stator field based on voltage and synchronous speed. The fundamental reason though is that using the RLA to get motor HP from the NEC Tables does not pass the "eyeball" test - meaning a motor compressor with 149 RLA would be 125 HP from the NEC Tables but looks more like a 40 HP induction motor in size.