1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Main Circuit Breaker in Panelboard

Discussion in 'System Modeling and Calculations' started by Jack, Sep 23, 2009.

  1. Jack New Member

    1200 amp 480v, panelboard, main circuit breaker
    Fed from utility transformer with only high side fuse
    The arc flash rating of the line side of the main is about 80 cal/cm2 based on 2 second clearing time (since the high side fuse will have a clearing time of never).
    The panelboard is the type that has seperate covers for the main circuit breaker and feeders, and therefore work could be performed on feeder breakers without removing the cover over the main lugs. It has a servance entrance label.

    If the main breaker was turned off, could work be performed on the load side of the breaker, such as adding a feeder breaker?
  2. Zog Well-Known Member

    Depends on the breaker type. Just opening a breaker is not sufficient for isolation purposes oer OSHA. A power circuit breaker needs to be racked out to the disconnect position and locked out for proper isolation.
  3. Jack New Member

    Main

    It's a molded case circuit breaker that is LOTO.
  4. JJH Member

    If the main is locked out and is in a separate compartment, there are no exposed energized conductors. You can install breakers or whatever. However at 80 cal/cm2, the problem comes when operating the 1200 amp main and verifying the absence of voltage.
  5. Zog Well-Known Member

    Operate the breaker remotely.