1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

limits on electric system

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by PUCKMAN, Sep 19, 2009.

  1. PUCKMAN Member

    Are there limitations to the size of the main elctrical system that can use the tasks tables for the arc flash study analyis? And if there is what size at 480 volt would be the limit where it is necessry to do a complete arc flash study?
  2. acobb Well-Known Member

    To use the tables, you first have to know if your system fits the limitations of available fault current and clearing time. You need this basic info from the utility to make the determination, irregardless of service size.

    Hope it helps,
    Alan
  3. WDeanN Well-Known Member

    Basically,
    Yes, there are limits. They are listed in the notes after Table 130.7(C)(9).

    What "size" 480V system would this be? No idea. There are two determining factors, one is available short circuit current, which could, sorta, be limited to an upstream transformer size, if you ignore several factors. The other is time, and is not affected by the "size" of the system, but by the protective devices used and how they are coordinated.
  4. PUCKMAN Member

    4000amp 480v . the main short circuit current is 100ka and the system s.s.c.is 85 ka. just read those numbers today off our system. 6 - 500kva trans. primery is 13.2
  5. WDeanN Well-Known Member

    Then you cannot use the tables on the 480V sections. The highest fault current the tables are good for is 65kA.