1. Create Your User Profile and Status Updates
    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum
    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!
    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!
    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!
    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.
    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!
    Learn More About the New Features Here
Units for E and En in Clause D.7
Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by Vincent B., Aug 21, 2009.
  1. Vincent B. Well-Known Member
    To which extent does NFPA 70E-2009 quotes correctly IEEE 1584-2002 in its Annex D?
    I ask because the Annex says both En and E is in J/cm^2, while because of the 4.184 factor in equation D.7.3(c), I believe it is possible that En is in cal/cm^2 and E in J/cm^2.
    Can somebody add their word on this, preferably quoting/verifying from IEEE 1584-2002?
  2. brainfiller Administrator
    You are correct! Annex D of NFPA 70E has the wrong units for En :( - it IS cal/cm^2. I am surprised this is still carried over into the 2009 edition. IEEE is required to use all metric so En in IEEE 1584 actually does not identify the units since it is not completely metric. It just uses the label "normalized incident energy". The units of Joules/cm^2 occurs AFTER you multiply by the conversion 4.184
  3. Vincent B. Well-Known Member
    So you multiply by 4.184 to get E in J/cm^2, then you divide by that same factor to choose your PPE in cal/cm^2. What a great way to have another Mars probe crash!
    At least, if you don't do the final conversion, you'll suit up too much, not too lightly. What a mess the opposite could bring up...
  4. chris kennedy New Member
    Appears someone should bring this to the NFPA's attention.
  5. brainfiller Administrator
    Pretty amazing, I know. :eek:
    --Chris K. yes it should be brought up. Conference Room 1 in the forum is where we have been attempting to hash out some language for proposals for the next edition of 70E. Guess we just got another one added to the pile.