1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Remote Racking - Open Air

Discussion in 'General Discussion' started by SCGEng1, Aug 12, 2009.

  1. SCGEng1 Member

    We have been discussing the following…evaluating remote racking as “open air†verses “in a boxâ€.

    We have several locations where remote racking is being used both on LV and MV breakers. The control cable is typically 20-30ft. The switchgear (metal clad) is remote racked either doors closed or open. The operator stands at some off angle (not directly in front) with respect to the switchgear. Adjusting the working distance, in the IEEE 1584 equations, to the control cable length is still producing incident energy values higher then we believe are truly possible at these distances. We would like to see some actual test data, video, or other evidence for this situation. If anyone knows of any please let me know. The test videos we have seen, with the doors closed, do not show a fire ball rolling out 20 or 30 feet. We have experimented with using the “open air†calculation at these distances, as expected the results are more favorable. Our thought is the arc blast will begin to spread out after leaving the box. It should being to dissipate in all directions after some distance due to it is no longer being directed and channeled by the enclosure. In addition, we think the breaker mass, enclosure, and door, even thought not arc rated, will provide some attenuation as compared to an open box with visibly exposed bus. Comments?
  2. Zog Well-Known Member

    Be very cautious with your assumptions, having lower Ei's won't be "favorable" to the person not wearing suffecient PPE.

    IEEE is doing some more testing and research I nelieve in this area so we will need to wait for those results. While I agree with your thinking until a good model exists you are stuck with the calculations available.

    But I can tell you another utility recently had an arc flash event on 15kV switchgear and the fireball enguled the whole room, operators are convinced they would have been injured or worse if they had been anywhere in that room. Lucky for them they were racking the breaker in with a wireless remote racking unit.

    It seems to me the best solution is to get a longer cable or go wireless.
  3. andeehunt New Member

    Though this thread is couple of months old, I think it will prove to be a good source of information to me.