1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Overhead switch arc gap

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by ekalbs4, Jul 9, 2009.

  1. ekalbs4 New Member

    When using IEEE 1584 Table 4, does an overhead switch on a utility 12.47 kV distribution circuit fall under the open air category or the switchgear category?

    I figure that open air is applicable and that switchgear is intended for enclosed type equipment, which this is not.
  2. acobb Well-Known Member

    If it is an open air break switch, then it shoud be analyized as open air.

    Alan
  3. acobb Well-Known Member

    And if it is utility owned open air equipment, I would use Arcpro and not 1584 for the numbers.

    Sorry for the double post.

    Alan
  4. ekalbs4 New Member

    Can you please explain why the preference for Arcpro?
  5. acobb Well-Known Member

    The open air calcs for over 1000 volts in 1584 assume a 3 phase fault. The NESC treats everything as a single phase fault because of the larger phase spacings. Arcpro was used to create the tables in the NESC and models single phase arcs in open air. We only use 1584 for enclosures and voltages less than 1000 volts.
  6. ekalbs4 New Member

    Great feedback, thank you very much!