1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Voltage Testing With Dangerous Category

Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by jghrist, Jul 2, 2009.

  1. jghrist Well-Known Member

    How do you establish an electrically safe work condition when the incident arc energy exceeds 40 cal/cm²? This sometimes occurs on the line side of 480 V main breakers fed by utility transformers that have no secondary protection.

    You could have the utility deenergize the transformer primary. There may or may not be a visible open disconnect when this is done. As I read 70E Article 120, you need to use a voltage detector to test each phase to verify that it is deenergized before working on the main breaker. Voltage testing is listed in Table 130.7(C)(9) as a task, so this would indicate that it is considered "interacting" with the equipment and would require PPE. How can the voltage testing be done?

    We've considered requiring voltmeters permanently connected to the line side of the main breaker, but Article 120 requires testing the voltage detector before and after each test to verify that it is operating satisfactorily. Before the test is OK - if the meter show voltage before the utility deenergizes the primary, the meter works. Then the voltmeter showing zero after deergizing is the test. How do you test a permanently connected voltmeter after the test?

    Would having the utility use a voltage detector on the transformer primary be satisfactory?

    Is manually tripping the main breaker considered "interacting" with it, thus requiring PPE for the line side arc incident energy? If so, how is this done when the incident energy is >40 cal/cm²?
  2. Zog Well-Known Member

    Reducing the Ei is the best way, or recalculate your Ei for the working distance the person will be at when doing the voltage testing.


    Yes, this is "interacting" with the equipment, remote switching is a popular solution for this.
  3. stevenal Well-Known Member

    Your high IE comes from the long duration clearing, not from an explosive release. You can suit up to the IE level even though it exceeds 40.
  4. elihuiv Well-Known Member

    This is a VERY common issue. The Danger on the label is decided on by the Arc Flash Study Engineer or the software not IEEE 1584 or NFPA 70E. They can all be WARNING labels if you so choose. I support Steve's contention above but remember verfication is the least risk method. You have to verify the absence of voltage so do it with a suit and with gusto and think of the folks who don't get to de-energize in the first place. They are the ones I'm concerned about.
  5. Zog Well-Known Member

    Well said!
  6. richxtlc Member

    The "Danger" is on the label not because an engineer or software has determined it to be totally unsafe to perform any live work, it is there because the danger is not from the arc flash, but from the arc blast. There are 100 cal suits available, all that means is that you will be buried with a good looking corpse.
  7. elihuiv Well-Known Member

    Dangerous Category

    Danger on the label IS decided by the engineer doing the study or by the software.

    100 cal arc flash suits have value IF you have long clearing times and low fault current or open air arc exposures where exploding parts, doors etc aren't an issue.

    I have seen suits take much more than that in a few instances and workers walk away with no injuries. Rarely does a worker receive the maximum calculated energy so flash suits >40 cal are life savers.

    The issue here is, IF I have deenergized, how do I do voltage testing. I THINK this circuit is dead BUT I have to test it and possibly ground it. Should be afraid because it says "DANGER"?

    My contention is that you can safely test.
  8. WDeanN Well-Known Member

    Thank you Hugh!
    I have been trying to tell people for years that just because it comes up over 40 cal/cm2 in the calculations does not mean it cannot be safely worked on. There is NO requirement to stop all work at 40 cal/cm in the NFPA 70E. They just don't talk about anything higher than that.

    Each situation needs to be assessed, and that includes times when the calculated energy is < 40 cal/cm.