1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

The Table and Switchboards.

Discussion in 'General Discussion' started by haze10, Jul 1, 2009.

  1. haze10 Well-Known Member

    The Table should have been constructed as a means to model typical US business industrial electrics.

    "Panelboards or Switchboards Rated >240 and up 600V with molded case or insulated case circuit breakers - Note 1"

    Note 1: Maximum or 25kA short circuit available, maximum 2 cycle fault clearing time.

    Wouldn't you say that 25kA is atypically low? How many 480 switchboards are there in US businesses that are fed directly from the utility transformer which are often 1000KVA, 1500KVA, and even 2000KVA? Why would they pick such a low value?

    Lets say we have something more typically industrial in the 35kA to 45kA range - what then. I take it we can't just use the 'switchgear' section whose footnote is max 65kA because it says 'power circuit breakers'.

    What is the economical solution to deal with switchboards at industrial fault levels. I'm talking the classic Square D switchboard, main breaker compartment with attached I-Line distribution panel.

    Further, lets say the fault is unders 25kA and there is a main circuit breaker. I think its safe to say that the utility is not using a primary fuse that will clear in 2 cycles for a secondary arc fault. So then we can't use the Table for the main. But if the main does clear under 2 cycles, can we use the Table on the distribution side of the cabinet? Is this prohibited because the fault on the load side of the main could carry over to the line side?