1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Arcing Current in the Instantaneous Band of Curve

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by GStalder, Jul 5, 2007.

  1. GStalder New Member

    I am performing arc flash calculations based on the IEEE formula's and I have a few cases where the calculated arcing current falls within the vertical instantaneous band of a molded case breaker's time current curve. Do I use the instantaneous time or go all the way up to the overload portion of the curve?? I assume worst case would be to use the longer time of the overload curve?
  2. K. Wilson New Member

    Arcing Current in the Instantaneous

    Your assumption is correct. For example if a breaker's instantaneous band goes from 900 Amps to 1200 Amps, it could trip instantaneously for currents begining anywhere from 900 to 1200. Thinking worst case you would use the 1200 Amps for the inst. This means currents of 1000, 1100 etc. may or may not trip in the instantaneous and you use the overload part of the curve.