1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Working on or near question?

Discussion in 'General Discussion' started by techman2512, Jun 9, 2009.

  1. techman2512 New Member

    Perhaps I am being too detail oriented, but in regards to both Shock & Arc Flash hazards and the boundaries associated with them; Do they apply only when working on that equipment or does it imply even being in the vicinity of that equipment. Example: We have some Med siz dry transformers that have an Arc Fault capable of > 40 cal i.e. over level 4. They have large vented panels that contain the transformer, yet, obviously they would not contain much blast, etc. Do we need to flag off our sub-stations so peolpe can't even walk by them. Example 2: We have some open bus that is protected against inadvertant touching, yet we have molded case circuit breakers hanging off the bus. The bus is rated at > 40 cal energy. Are we not even allowed to walk in this room? Example 3: We have feeder breakers rated at >40 cal. We have decided because of that energy to open the primary switch feeding that breaker before doing any work on those breakers....sounds practical until we have to try and verify Electrically Safe on the feeder breaker before we can work on it. Since it is No FR Class found work, how do we even approach verify all the steps for Electrically Safe??
    Thanks,
    Mark Blau; NewPage Corp
  2. Zog Well-Known Member

    First thing I would look at is some mitigation, you have some pretty hazardous areas there and reducing the hazard is the nest solution.

    That said, the 70E refers to "interaction" with the equipment as to when you need to wear PPE. So for examples 1 and 2 you do not need to wear PPE to walk in the rooms. However example 2 has some access issues per OSHA for who can enter the room and what thier qualification needs to be.

    Example 3, tough one, lots of plants have this issue. Best thing is to use hotsticks to verify the equipment is dead, increasing distance will reduce the hazard level to a managable level.