1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

PPE for 120V receptacle?

Discussion in 'Electrical Safety Practices' started by MIEngineer, Jun 4, 2009.

  1. MIEngineer Member

    In NFPA 70E (2009) Table 130.7(C)(9) states "Work on energized electrical conductors and circuit parts of utilization equipment fed directly by a branch circuit of the panelboard" has an HRC of 1.

    Does the common interpretation of this mean that work done on a 120V receptacle requires HRC 1 PPE?

    The energized work I speak of is for troubleshooting or testing. I don't see a reason to perform non-testing energized electrical work on a 120V receptacle.

    As always, thanks.
  2. PAult Member

    This is my interpretation....

    A quick arc-fault calculation will probably reveal that this is fed from a transformer that in less than 125KVA. Since it is less then 125KVA, no arc-fault calculations are required and you can label this as HRC 0.
  3. THE CABLE GUY Well-Known Member

    Gloves?

    If you speak of Class 0 gloves PPE shock protection for 120v? There are a few opinions on this that I have found in the past. I cannot find the link but, there is a letter of interruption that comments on using gloves on 120v ac. Say for testing a receptacle outlet with a meter. Example of exception was test leads that would stop the fingers from slipping and touching the probe tip and no other components in the area that can be touched etc.. The key I suppose is the prohibited approach area for shock protection. In this case, do not touch.
  4. chris kennedy New Member

    A receptacle is a contact device and not utilization equipment.

  5. THE CABLE GUY Well-Known Member

    MIEngineer,
    This is the link to what I was speaking too earlier it’s not OSHA but is by BNL Electrical Safety Committee interpretation.

    I believe the word PANEL is referring to 3phase 240 volts or less and the device is a panel board say for lighting, heating, hvac etc. As mentioned by Chris. I reach this conclusion because, AF hazard is calculated by using 3 Phase short circuit data in the formulas used to determine the hazard level.

    My interpretation of this is not of a receptacle but a three phase circuit breaker feeding a device such as a heater or HVAC system. And the person is working with such equipment.

    Moreover, the statement by, PAult I agree with. If the exception is met then you must only be concerned with shock hazard.
    +
    http://www.bnl.gov/esh/esc/PDFs/Use%20of%20Voltage-Rated%20Gloves%20-%20120V%20Single%20Ph.%20Circuits.pdf