1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Motor Starter MCC

Discussion in 'General Discussion' started by jjakubin, Jun 3, 2009.

  1. jjakubin New Member

    I performed arc flash calculation using IEEE 1584 on a 480 volt three phase motor control center (MCC) and the incident energy level exceeds 1.2 cal/cm^2. Does the calculated value negate allowing an individual to perform a circuit breaker or starter operation with the enclosure door closed at a hazard risk category 0 based on Table 10.7(C)(9)?
  2. haze10 Well-Known Member

    Flame question?

    MCCs are not switchgear and outside of the intent of high energy switching devices. With doors closed there are no exposed and energized components. Hence, NO PPE is required. If you want to use HRC0 thats higher than 'none' so go ahead.
  3. jjakubin New Member

    Thanks for your reply.
    Correction to my original post:
    I'm referring to table 130.7(C)(9) under section (600v Class Motor Control Centers (MCC's) Note-2)

    For example, we calculated incident energies on our 15kv switchgear and the energy levels are at Catagory-2. Per Table 130.7 (C)(9) (Metal Clad Swtichgear 1kv through 38kv) insertion or removal of circuit breakers from cubicles doors opened or closed is Catagory-4.

    Is it acceptable for the task of insertion or removal of circuit breakers from cubicles doors opened or closed to wear catagory-2 PPE even though the table differs? If this is acceptable because of the calculated incident energy values, why would'nt the calculated energy values dictate the PPE clothing for 480v MCC's.

    Do we follow the table or we follow our calculations?
  4. Zog Well-Known Member

    Yes, the tables are based on many assumptions and tend to fail on the safe side (More PPE). If your calculated Ei is <8cal.cm2 you can use HRC 2 doors open or closed.

    It does, once you have done the study you should follow those PPE requirements.
    Calcs.
  5. haze10 Well-Known Member

    You have your choice of following either of two methods: under IEEE 1584 you calculate the IE at the point of interest and then use one PPE for all tasks; under NFPA Task Matrix you do NOT calculate IE at the point of interest and vary that PPE according to the table for a particular task. With the Table you need to verify Isc and OCPD (overcurrent protection device) clearing times are within the limits of the NOTES. You should not be co-mingling them together as that just creates the confusion you are experiencing now.