1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

What is the range of E and En?

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by abbhas2009, May 27, 2009.

  1. abbhas2009 New Member

    Hi:
    Would you please help to get the expected value for E & En for 480V in-box switchgear? We were trying to use the IEEE 1584 formula
    Log En = K1 + K2 + 1.081 * Log Ia + 0.0011 * G AND
    E = 4.184 * Cf * En * (t/0.2) * (610^x/D^x).

    I (bolted fault) = 40kA.

    If we got Log En = 515, would that be correct? and what is En?

    Thanks,
    abbhas2009
  2. Mike Frain Administrator

    Good to see somebody using the calculations long hand (manually). En is the normalized Incident Energy for an arc duration of 0.2 seconds and for a distance of 610mm. The second equation that you show is to adjust this normalized figure to the actual duration and the actual distance to the worker. I'm not sure where your figure of 515 comes from for Log En, seems very big to me. I suspect that you've not considered that the K factors are negative numbers or perhaps you've misplaced a decimal point somewhere. If you log onto the link below, Jim Phillips provides really easy step by step work sheets for the calculation of arcing current, incident energy and flash protection boundaries. (They are free plus lots of other very useful material as well)

    http://www.brainfiller.com/newsletterArchive.php
  3. abbhas2009 New Member

    What are the values of E and En?

    Hi Mike,

    Thank you, we had considered the minus, however, the voltage was incorrect (480 was corrected to 0.48). The new result for Log En, En and E is 0.77, 5.93 and 3.72 respectively.

    When we changed the bolted fault current to 106kA, the results got higher a little up to 1.15, 14.27 and 8.98.

    E: in J/cm^2

    Have a nice day,
    abbhas2009
  4. jghrist Well-Known Member

    You haven't shown the calculation of Ia (arcing current) from Ibf (bolted fault current) using IEEE-1584 Equation (1).

    I can't get your numbers using either the arcing current or the belted fault current.
  5. abbhas2009 New Member

    Values for En and E

    Hi jghrist;

    It is the same equation for IEEE 1584. We believe that the values are coming reasonable.

    Regards,
    abbhas2009