1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Line Side Main Breaker >40cal

Discussion in 'General Discussion' started by LAS, May 26, 2009.

  1. LAS New Member

    I recently completed an arc flash study where the line side of a main breaker in 480V metal enclosed switchgear has an arc flash hazard category of Dangerous because the upstream protection is located on the primary side of a step down transformer. The remaining portion of the 480V switchgear including the load side of the main breaker, three feeder breakers as well as the vertical and horizontal bus all have a category of 3 because the main breaker is able to clear the arcing fault in a timely manner. The switchgear consists of two sections, an incoming 32" wide section housing the main breaker and a 22" wide section containing three feeder breakers.

    What if a person is performing electrical work in the 22" wide feeder section, and an arcing fault incident occurs on the line side of the main breaker in the incoming section that is labelled as category Dangerous?

    Altough the probability of this happening is low, I would like to determine how the code addresses this scenario or identify what the best practices are for this situation. Currently the interpretation of the code and best pactices are unclear to me when applied to this example. If the worker is not directly working on the line side of the main breaker does category Dangerous and associated flash protection boundary still apply? Should the 480V switchgear be labelled on a cell by cell basis or should it all be labelled as the highest category? For example, should the incoming section be labeled as Dangerous with the feeder breaker section labelled as category 3 or should the entire switchgear assembly be category dangerous? Note that my calculations show that the flash protection boundary associated with the main breaker being category dangerous, encompasses the entire switchgear assembly.

    Thanks,
  2. MikeMc New Member

    1. OSHA says don't work on it live unless there is no other way. Based on the danger to the equipment (not even counting the personnel) why take the chance?

    2. Use current limiting fuses in the primary side of the transformer, this will reduce the hazard.