1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Questions on How to Handle

Discussion in 'System Modeling and Calculations' started by levans, May 19, 2009.

  1. levans New Member

    I am doing my first arc flash hazard analysis and I am using EasyPower software. I have two questions:

    1. I have an area in the plant that has 480VAC bus duct that has multiple fused disconnects attached. This bus duct is elevated above the floor about 12'. How do I show this in the software and how do I label this equipment?

    2. I have an area that over the years instead of buying a mcc, the customer has just added more fused disconnects and combination starters. These are all mounted side by side and vary is sizes. The software covers how to handle a mcc, but I don't know how to handle this arrangement? How do I label (each device, in the general area?)?
  2. Mike Frain Administrator

  3. SPETE New Member

    Our main bus duct is 300' I've split that into 20 or 30 foot sections depending on the number of taps coming off and labled each bus with the distance....bus 3/ 20-40...
    bus 3/ 40-60 etc. Each section is a node. Hope this makes sense.
  4. THE CABLE GUY Well-Known Member

    I use the software every day. This is what I do but for every engineer a different way exist.

    1) Model the busway and length.
    a. You can do multiple lengths or model each section of busway.
    b. Enter a bus between each section or groups of busway section.
    c. Enter the bus tab type as Busway, and material.
    2) Model the system the way it is.
    a. Model the busplug's fused switch (or whatever) and enter fuse data.
    b. Model the wire and conduit to the floor device.
    c. Model the floor device say another fused switch , enter protective device data.
    d. Model the wire and conduit to the load.
    e. Model the load. Motor? or Heating or other for each device or use an MCC if there are multiple components on the load side. This will help you also with FLA and protective device design if needed.

    If you place a bus before the fused switch on the floor that will reflect the load side AF. If you place a bus after the fused switch that is the Load side AF. I label the fused switch with the highest hazard of the two points. I also label downstream electrical control enclosures as needed. You can modeling the enclosure as a bus (node) or another protective device.

    When in the bus data tab, select type panel and material type.

    Hope this helps. It's the best way to accurately model your systems hazards. If you need more assistance let me know.
  5. levans New Member

    Thank you for the information. Any chance that you might have an EasyPower project showing an example of this that you could send me?
  6. THE CABLE GUY Well-Known Member

    levans,
    I sent you a message off the forum.
    Thanks
  7. Homerjs78 New Member

    EasyPower example file

    You may try asking EasyPower tech support your question. They have example onelines that show exactly how to model the busway. It involves grouping motors into 10' to 20' sections. There is no reason to model less than 10' due to very small impedance values that cause rounding errors. Give them a try.