1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Work in Manholes and PPE

Discussion in 'Electrical Safety Practices' started by 321Liftoff, Nov 19, 2007.

  1. 321Liftoff New Member

    We are having a debate about what PPE is required when working in manholes. Are the Medium Voltage (13.8kV) cable splicers allowed to work in a manhole with category 1 (preferred) or 2 PPE to perform the splice even though there are other live MV cables in the area?

    The manhole is inspected first wearing Cat 2 PPE and the Feeder Breaker relay settings are set low (hair trigger) for all cables within the manhole, prior to entrance for any activity.

    The obvious problem we are having is not wanting to wear excessive PPE down in the manhole.

    How have people been handling this?
  2. LaszloZW Member

    So what is the work that exposes the worker to an arc-flash potential?

    If cutting into potentially live cables is the only hazard, in the case of a manhole confinement I would do that with a remotely operated hydro cutter.

    After that no arc-flash hazard associated with their work would exist.
  3. haze10 Well-Known Member

    The way I approach this is as follows:

    1) There is always a confined space permit and and an electrical safe work permit.

    2) electrician enters manhole in Level 3 with tic tracer to check for voltage.

    3) If no live voltage found, electrician exits and then dresses down to Level 2, which is their normal attire, with only safety glasses and hardhat.

    The thing to remember is that PPE is only for 'live' work or near live work. Inside the manhole there is no live parts, yes, there may be energized cables, but they are fully insulated for the service. A cable splicer is not exposed to any live parts and as such no PPE at all is required.

    The same can be true for an electrician that opens a wireway in a MCc line up to take a amp reading, or pull through wire for another project. There are no exposed live parts in the wireway.

    I am not advocating no PPE level, ie, you would not want to ever be in polyester clothing doing any electrical work. But you could be Level -1 or 0, or as we do normal work attire is Level 2.
  4. Zog Well-Known Member

    Great question, I have agood solution, the last company I worked for did dozens of MV splices a day, so I had to research and devise a solution, granted it is not perfect, but it combines safety with workability.

    1. Do all the manhole entering stuff that has nothing to do with arc flash (Confined space rigamaroll)
    2. Don 40 Cal suit
    3. Enter manhole, wrap other cables with arc flash suppression blankets
    4. Exit manhole, get some air, don HRC 2 PPE
    5. Re-enter, work in HRC 2