1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

VFD driver

Discussion in 'General Discussion' started by Noah, May 8, 2009.

  1. Noah Member

    Hello, we often find VFD, UPS devices in the distribution system. Normally how do you evaluate the fault contribution from these devices? I was told that usually we can use 200% of the FLA, is it right? How do you deal with the by pass? Thanks!
  2. haze10 Well-Known Member

    VFDs are inherently current limiting . 200% of FLA is a good number. For a UPS it would depend on the type, a double converion (AC to DC, DC to AC) would be SCR based so the same 200% would be good. Ferroresonant UPSs might be a little more but still pretty low because of the high impedance. Bypass switches, the electomechanical kind, would be like any other conductor. You'd have to calc for when fed from utility and for when fed from UPS, but they would not be current limiting and you would calculate at the point where the line cables land on the switch. If the switch is triac based it would be current limiting but that would only play in downstream of the bypass as the line cables would still be landed on the line side of the switch.
  3. Noah Member

    Thanks Haze!