1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

2009 nfpa 70e annex d d.7

Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by 480V, May 7, 2009.

  1. 480V New Member

    Can anyone explain why D.7.1 system limits are listed as 700A to 106,000A availible short circuit current.

    Then D.7.6 (H) says that if Ibf is <.65kA, calculate the arcing current per Equation D7.2.(a),and use time -current curves to determine incident energy using Equations D.7.3(a),D.7.3(b), and D.7.3(c).The system limits in D.7.1 seem to apply to Equations D7.2.(a),D.7.3(a),D.7.3(b),D.7.(c)?

    I have a situation with bolted fault current below .7kA

    Thanks
  2. brainfiller Administrator

    Great Question!

    Two different things happening here.

    D.7.1 is from IEEE 1584 and is the range of vailidy of the IEEE 1584 standard. i.e. calculations closely match the tests in this range. If the short circuit current is outside the range, most software will still use the formulas but with language that it is outside the range. For your case of a low short circuit current, using the formulas is still probably about your only option. - but I bet the protective device clearing time will be interesting!

    D.7.6(H) is for Class R current limiting fuses up through 100A. There are other formulas for larger fuses and other classes. For RK1 up to a 100A rating, below 650 Amps (0.65 kA) the fuse is considered to not be in its current limiting region and therefore treat it as a non current limiting device i.e. use time current curves.

    Above 650A a series of equations were developed based on a few tests to see what happens with let thru current, arc voltage etc. The 650 Amps lower limit of this specific equation is due to the small size of fuse for this case - 100A max.

    However, you picked up on something I have not considered, the 650A limit of the RK1 fuse < 700A limitation of IEEE 1584 - oops! :eek: I believe it is only for the smallest fuse - I don't think I would get too excited over 50 Amps - there are plenty of other areas that are more troublesome.

    I'm thinking after the fuse tests were run and equations were developed, the low limit cut offs of the fuse equations were developed (650 Amps for RK1 100A max) even though it techincally falls below the overall 700A low limit of the IEEE 1584 document.