1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Hc4 ppe

Discussion in 'Personal Protective Equipment (PPE)' started by TxEngr, May 7, 2009.

  1. TxEngr Member

    The 70E states that HC4 PPE is "Arc-rated FR shirt and pants or FR coverall, and arc flash suit selected so that the system arc rating meets the required minimum" (Table 130.7(C)(11)). Since I normally wear HC2 clothes anyway, I never really put much thought into this. But in looking at it closer, do you think it is acceptable to wear HC0 clothing under a flash suit that is rated for 40 cal/cm2? This "system" meets the required minimum but does not include the FR Shirt and pants called out in the description. Comments?

    TxEngr
  2. haze10 Well-Known Member

    I've wonder the same question. The code clearly states that its purpose is to limit skin exposure to 1.2 cals. FR clothing is tested to limit internal exposure to 1.2 cal (but only at 50% probability). I talked with an Oberon exec once who told me you could be in your underwear as long as the clothing met the IE level.

    The arguement could be made for which method you choose, IEEE or Table. If you do the analysis, the obligation is for the clothing to meet or exceed the IE, and that could be with just the one outer layer. If you conform to the Table method, then the arguement could be made that the additional layers are specified in the HRC definition so they are required.