1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Taps on Transformers

Discussion in 'General Discussion' started by LarryJo, Apr 28, 2009.

  1. LarryJo New Member

    Do the tap settings on power transformers affect the ARCFLASH study enough for us to be concerned with them?
  2. haze10 Well-Known Member

    Voltage is a variable in the ieee formula for calculating arcing current. So it would have some effect. You'd have to run the equation with the different tab positions to see how much. My gut feeling is that it won't have a big difference, but not sure.
  3. jghrist Well-Known Member

    The problem with accounting for taps is that there is no formula to determine impedance at different taps. Unless you have the test data on different taps, you can't accurately calculate the fault current.
  4. Gary B Well-Known Member

    Large power transformers generally are sold with impedance at tap settings, but that information is probably long gone by the time an arc flash study is being conducted. One could theoretically include both extremes and study the effects at each location on downstream distribution system, but managing such a study will point out that perhaps the methods should include a little compromise for sake of practicality.