1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Tables vs. Analysis

Discussion in 'General Discussion' started by Vica1ME, Mar 30, 2009.

  1. Vica1ME New Member

    130.3(A)(2) gives the parameters for the Arc Flash Protection Boundary when above 1000 volts. The FPN steers me to Annex D for estimating the boundary. Are there any default numbers for voltages above 1000 volts? If not, must this boundary be calculated? Thanks!
  2. Vincent B. Well-Known Member

    Basically, yes.

    So then, you'll say "what's the point of using Table 130.3(C)(9) for tasks above 1 kV"? No idea.
  3. McFlash New Member

    I think that you are talking about table 130.7(C)(9).That table has nothing to do with the Arc-Flash Protection Boundary. It deals with tasks once you are inside of that boundary. You need to calculate the boundary to properly apply table 130.7(C)(9).

    I am in no way promoting the tables but if you are going to reference them and use them you must follow all application guidelines......meaning following all notes and FPN's as well as first establishing the proper boundary distance.