1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Reduce incident energy by lowering instantaneous trip setting

Discussion in 'Equipment to Reduce Arc Flash Dangers' started by beenthere, Mar 26, 2009.

  1. beenthere New Member

    I intrepret NFPA 70E110.9(D) to allow me to reduce the instantaneous trip value of a circuit breaker, as done in device coordination, to also reduce incident energy.

    What keeps me from reducing to a minimum value (with calculations done) to a minimum when performing work and then resetting when done.

    There are add on devices now on the market that do just that.
  2. acobb Well-Known Member

    We generally refer to those as maintenance settings for the specific purpose you are asking about. Depending on the breaker and associated overcurrent protection you have, it might have an alt settings available. If so you can use the front panel or an external switch to enable them once configured. You could lower your pickup, time delay, and inst. if necessary. And you are correct about the other devices available if your relay does not allow it.

    You could also look at the entire facility (if practical) to see if you could modify the settings permanently as they may be elevated now just to insure against nuisance tripping without regard to arc flash issues.

    Don't usually like the idea of "dialing it down" by hand since it may not get back to the correct setting after the work is done.

    There are other posts here about this very issue if you can find them.

    Hope it helps.
  3. beenthere New Member

    Thanks for the reply

    Good points. I would not suggest this to our guys just seems too easy and too easy to make the wrong assumptions once the setting is made.