1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Exposed or NOT???

Discussion in 'General Discussion' started by Jnox, Mar 16, 2009.

  1. Jnox New Member

    I'm sure this has been mentioned before, as it is a big issue. I couldn't find anything that would directly answer my questions. Maybe you guys could help. (brainfiller????)

    Since NFPA likes to be vague on certain things, let me bring up few questions regarding "Exposed Live Parts."

    Here are three different scenarios:

    1. 480V MCC Rated at Arc Flash LVL 3 PPE when working on Energized Parts.

    Pull the Disconnet - LVL 0 (according to NFPA 70E 2004 130.7(C)(9)(a) table)
    Verify circuit is de-energized LVL 3.

    Once verified, okay to perform work without PPE on? This is a debate considering only the top of the disconnect has live parts and you'd have to use something small like a screwdriver to get to it. Is there anything in OSHA, NFPA that says it is NOT okay to work without PPE or is this still LVL 3?

    2. 4160V Switchgear with Arc Flash LVL 3 PPE when working on Energized Parts but with breaker REMOVED and shutters closed.

    Since the shutters are closed, is it still LVL 3? Technically, since the shutters are closed, you do not have anything "exposed." What about control circuit (ex. 125V DC)?

    3. 4160V Switchgear with Arc Flash LVL 3 PPE when working on Energized Parts but with breaker in service (or racked out for that matter).

    When you open the cubicle, NO live parts are exposed unless you deliberately defy the safety mechanism. Is this still LVL 3, or no Arc Flash protection required.

    HELP!!!!!!
  2. Zog Well-Known Member

    You are still working withing the arc flash boundary of the live parts, even though you are not actually working on the live parts. My interpretation is that if you are withing the AFB then you still need the same PPE. I feel that this is overkill myself but the intent of the 70E is to eliminate any type of electrical work. I agree this is a grey area.

    The arc flash hazard still exists, you are interacting with the equipment and the hazard is still there. Working on control circuits in that cubicle could cause another breaker to trip or close and intiate an arc, I wouldnt want to be in a cell when that happens, shutter or no shutters. However, you can argue that you can use reduced PPE per the tables (HRC 2 in this senario), that jives with the HRC 2 requirement for operating the breaker with the door closed. Are you using the tables or have you done an analysis?

    That breaker has nothing to do with the arc flash hazard in that cubicle, it is the upstream breaker (or fuses) that determine the hazard level, so still HRC 3 if that is you calulated value, in fact it may be higher, chances you arc flash analysis assumeed a working distance greater than where you would be working when in the cubicle, so the Ei may be even higher than your label.
  3. stevenal Well-Known Member

    I'm confused about question 3. How do you work on energized parts without exposing them? Can you be specific about the nature of the task you have in mind?
  4. Jnox New Member

    That's a good point. Looking at the table provided it tells you can pull the disconnect with LVL 0 PPE. When you do that, you are also within AFB. At the location where I work, it will be very difficult to convince people it is a shock hazard. If we interpret this as a safe enough situation, will it violate any regulations, or is it completely up to us?


    I have performed the analysis. Not completely done, but for the most part I am. Since I have performed an analysis, can I still fall back on the table in NFPA?

    I am assuming, to perform work inside that cubicle, we need to kill the main to that switchgear?

    For this particular switchgear, I have calculated Main incoming breaker as DANGEROUS. The rest of cubicles came out to be LVL 3. Since in this situation, the fault would be compartmentalized, that is the way I will label each cubicle. I guess my question was, if I just open the door to look inside the 4160 switchgear, even though there are no "directly" live parts, I still need to have PPE on? I think I have an idea what the answer will be to this one ;) .

    All of this makes sense, but then it also doesn't demanding on the situation. The hard part is convincing people this is the way it's supposed to be given you can't say "it's the law" since NFPA is very vague on this subject. What a pain in the arse.

    Good comments, keep them coming people!
  5. Jnox New Member

    I should probably rewrite the question. Essentially, what I'd like to know is, when you just want to peek inside the cubicle, do you need PPE on?

    Most of the MV/HV switchgear, when you open it up, there is no LIVE parts directly exposed. It is all in the back of the switchgear. I have been asked, if this is the case, why need for PPE since you will not work on any live parts?
  6. Zog Well-Known Member

    The shock hazard exists (Per 70E) if you are working within the LAB of exposed live parts, regardless of "what" you are "working" on.


    The 2009 70E has verbage that strongly advising against mixing the use of your calcs and the tables. Once you have doen the calcs you have aknowledged the hazard level and to reduce PPE vis the tables would put you in a tough situation with OSHA should an accident occur. Remmember the tables are more or less "gut" feels of the 70E commitee and you analysis represents the real hazard more accuratly than the tables do.

    Good question, as a person that spends a lot of time doing exactly the same thing, I always try to de-energize if possible. Is this as hardous as working on the 4160V, yes and no.

    Yes, the some potential arc energy is there, even if it may be partially absorbed by the enclosure, but then again the pressures will build up more in an enclosed environment and can be higher than if the arc was in open air, IEEE 1584 is doing research as we speak on pressures, our host here is involved and has posted some of that info on this forum.

    No, even though the hazard is the same (Or maybe worse) the risk is reduced, less chance of initiating an arc.



    Agreed, but the "law", and by that I mean OSHA, will look at your study results and question why PPE wasnt worn when the hazard was calculated and acknowledged. Sorry I cant give you anything more solid, sounds like you have a good understanding on the subject, do what you feel is right.
  7. Vincent B. Well-Known Member

    It's not a shock hazard, but it still is an arc flash hazard, hence your lookup in the table and the usage of arc flash rated PPE.

    From NFPA 70E 2009, 130.3 Exception No. 2:
    My understanding is that you can use the tables (watch for the notes), but if you actually do a detailed incident energy analysis, then you can't go back to the tables (especially if the tables allow you to use a lighter PPE than your detailed analysis).

    Now, for another equipment, one for which nobody did a detailed incident energy analysis yet, then the tables are good to go (again, watch the notes).

    "But the tables don't have the same PPE requirement for different tasks on the same equipment, while a detailed incident energy tells me to wear the same thing for a specified working distance!"

    Short answer: Yes, it's true.
  8. Zog Well-Known Member

    No exposed live parts here either, would you have wanted to be in front of this switch?

    Attached Files:

  9. Gary B Well-Known Member

    There looks to have been exposed energized parts in that switch and we do not know what triggered the event.

    In general we do not require arc flash ppe to look inside switchgear, providing it is a 'look' and not 'touch' and there is nothing that might disturb the electrical field. That is 'in general' but there are also conditions such as excess spider webs, rusty or loose switchgear componentes where merely opening the door might constitute disturbing the electrical field.
  10. Zog Well-Known Member

    The 70E tables now have reduced PPE requirements for visual inspections, but you still need PPE to do so.
  11. MikeMc New Member

    I was waiting for this one. Kind of like peeking inside of a bomb to see if it is armed.

    What about the next guy who just wants to peek inside and it turns out to be a tie breaker cabinet with 15 kv on the top and bottom. Breakers is off but is there any voltage inside the cabinet. You tell me.

    The rules are written to try and protect people from themselves. Of course if we do away with OSHA and NFPA then the problem eventually becomes self correcting.