1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Conversion error in CSA Z462-08 Annex D?

Discussion in 'CSA Z462 Workplace Electrical Safety' started by Vincent B., Mar 4, 2009.

  1. Vincent B. Well-Known Member

    Hello there,

    In equation D.5.2(a) of Annex D of CSA Z462-08, the exponent of D_A is -0.9246. In equation D.5.1(a) of Annex D of NFPA 70E 2009, it's -1.9593. The two following sample calculations give the same Incident Energy given the same input data.

    All this seem OK, until you try some other value of D_A with both equations. Then you don't get the same results.
    Somebody fuddled with the exponent of D_A so the sample calculation worked out OK, but you can't do that as all other values of D_A won't give you the same results.

    I propose the following to replace equation D.5.2(a) of Annex D of CSA Z462-08:
    E_MA = 5271 x 25.4^1.9593 x D_A^-1.9593 x t_A x [0.0016F^2 - 0.0076F + 0.8938]
    which could be simplified in
    E_MA = 2981000 x D_A^-1.9593 x t_A x [0.0016F^2 - 0.0076F + 0.8938]

    Also, in CSA Z462-08, the definition of D_A for equation D.5.2(a) says it's in inch, when it should be in mm.

    The same conversion mistake has been made in equation D.5.3(a) of CSA Z462-08. I propose the following to replace equation D.5.3(a) of Annex D of CSA Z462-08 (once simplified):
    E_MB = 587460 x D_A^-1.4378 x t_A x [0.0093F^2 - 0.3453F + 5.9675]

    Any comments on this?
    To who should I report this?
  2. Vincent B. Well-Known Member

    A typo this time...

    In D.7.3 of Annex D of CSA Z462-08, the definition for K says:
    In D.7.2 of Annex D of NFPA 70E 2009, the same definitions for K says:
    I don't have IEEE 1584 to compare what that standard says.

    To who should I report this?
    Thanks.
  3. stevenal Well-Known Member

    1584 agrees with 70E.
  4. Vincent B. Well-Known Member

    So CSA Z462-08 is in need of a correction.

    I'll look into how to do this.
  5. Terry Becker Member

    Vincent:

    I am on the CSA Z462 Technical Committee, next meeting is in Regina, April 1-2.

    We are treating all comments as formal requests for clarification, we need this to happen.

    Can you email me your comments so I can follow up formally

    Regards;
    Terry Becker
    www.esps.ca
    terry.becker@espsi.ca
  6. Vincent B. Well-Known Member

    Sure Terry. I'll do it so we get a better CSA Z462 in the end, one we can trust.