1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Question on a size of Arc Flash

Discussion in 'General Discussion' started by Willis, Feb 19, 2009.

  1. Willis New Member

    Does anyone know what the results would be from a simple small distribution disconnect if it were short circuited and it had an arc flash. How large and destructive of an arc flash could this small of a device actually create?
  2. Zog Well-Known Member

    Depends on the available fault current and the clearing time of the protective device. Could potentially be a devesating arc flash that can destroy the equipment and injure persons anywhere in the room, or could be very minor and not dangerous, all depends on the factors involved.
  3. Noah Member

    For small disconnect switch, sometime it is hard to find space on the switch to put a lable on. How do you guys deal with those devices? What if you have a row switches on the wall for pump/motor control?
  4. Willis New Member

    Clearing time

    What do you mean "clearing time"?
  5. Zog Well-Known Member

    How long it takes the fuse or breaker to clear the fault at different fault current levels.
  6. Willis New Member

    Thanks!

    I appreciate the information Zog.
  7. Zog Well-Known Member

    Welcome to the forum.
  8. WDeanN Well-Known Member

    How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
    If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
    We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.

    Noah, if there is a wire trough above the disconnect rack, I would consider putting the label there, although I have also covered the factory markings at times (I do my best not to, though.)
  9. Willis New Member

    How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
    If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
    We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.


    What is the cal/cm range that an arc flash becomes deadly or cause serious injury?
  10. Zog Well-Known Member

    1.2 cal/cm2 will cause second degree burns in 1/10th of a second. Put you in a burn unit, life changing event.