1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Maintenance Settings to Lower HRC and IE

Discussion in 'General Discussion' started by McFlash, Feb 12, 2009.

  1. McFlash New Member

    One thing that we have developed within our company are maintenance settings to lower hazards on equipment. Using PDC analysis we adjust settings, usually just instantaneous settings to the proper level to have an acceptable working level. Of course this throws coordination out of whack but we are using it solely when energized work is going to be done. Than the settings are set back after work is accomplished. My question is has any one else seen this or are practicing this? Is there any flaw in our reasoning that we are overlooking?
  2. Zog Well-Known Member

    Very common concept, but typically done using a maintenence switch, like the Quick Trip system. That way it is comtrollable, we prefer the quick trip becasue it has a padlockable switch cover. We retrofit breakers with these systems all the time.
  3. wbd Well-Known Member

    Ditto to what Zog says. Without a specifically dedicated maintenance switch that will implement the maintenance trip settings, you have to have a strong policy/procedure/controls to insure that the settings are returned to the proper settings for coordination.
  4. Zog Well-Known Member

    I fthey dont get returned to the right settings, and it will eventually happen, and the plant trips off line because of it, well you know, let the blame game begin!
  5. McFlash New Member

    Any links to manufacturers of the quick trip system your are referring to??

    Thanks for the comments too.
  6. Zog Well-Known Member

    www.utilityrelay.com
  7. dpmac New Member

    Depending on your breaker type, needs and your budget, in addition to many retrofit kit companies, many of the manufacturers offer some type 'Maintenance Trip" or "Arc Safe" kind of system.