1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

SKM PTW Miscoordination

Discussion in 'Software for Arc Flash Studies' started by ZeroSeq, Feb 2, 2009.

  1. ZeroSeq Member

    Miscoordination is not necessarily a bad thing.

    I struggled to eliminate miscoordination errors from my Arc Flash Studies until I spoke with Jim Babcock at SKM. Jim teaches their Arc Flash seminars.

    Traditional protective relay studies are based on Isc, three phase bolted fault currents. In reality most real life faults are less than Isc, especially arcing faults. IEEE 1584 uses 85% of Isc. NFPA 70E uses 38% of Isc.

    What the "(*N5) Miscoordination, Upstream Device Tripped" message indicates is that an upstream device (fuse or relay/CB combination) interrupts the fault before the device closest to the faulted bus. That's good, compared to not clearing the fault at all. It's a situation you may want to address with your protective relay specialist. There may not be a perfect solution that properly protects for both Isc and arcing faults.
  2. Noah Member

    Thanks for sharing!
  3. Gary B Well-Known Member

    Nice to have a reality check.

    Because we are calculation for worse case exposure it is compelling to get swept up in worse case fault thinking which may not be realistic.