1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

208V equipment fed from 750kva 600/208V transformer

Discussion in 'System Modeling and Calculations' started by J.T, Jan 30, 2009.

  1. J.T New Member

    I am a new member. Please let me post a question.
    IEEE 1584 states:"Equipment below 240v need not be considered unless it involves at least one 125kva or larger low impedance transformer in its IMMEDIATE supply"
    My case: 750kVA 600/208-120V 7.1% transformer supplys 208V switchboard A. Switchboard A supplys 208V panel B via cables, and panel B supplys another 208V panel C via cables. I need to do arc flash analysis for switch board A based on IEEE 1584. Do I need to do arc flash analysis for panel B and C? Or just label panel B and C according to NFPA 70 table 130.7(C)(9)(a)? I do not think the 750kva transformer is immediate supply to panel B. C. Thanks!
  2. RECS New Member

    I don't think that the transformer is Panel B or C immediate power supply. I understand that the calculation is not necessary.
  3. stevenal Well-Known Member

    The same standard says "The arc-flash hazard need only be considered for large 208 V systems: systems fed by transformers smaller than 125 kVA should not be a concern." No "immediate" qualifier there. Also note that NFPA avoids the "immediate" qualifier.

    Also see http://www.arcflashforum.com/showthread.php?t=324
  4. haze10 Well-Known Member

    YOU don't have to list the the HRC Task Matrix. Since it is outside the analysis,, you can just list a single HRC of 1 or 0 for all tasks.