1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

2009 70E 130.3 Exception 1

Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by psThomas, Jan 16, 2009.

  1. psThomas New Member

    Our facility uses 25kVA transformers (480 to 120/240v) for control power for discrete I/O controls. This is an example of meeting Exception 1 in section 130.3.

    The tables suggest that performing a voltage test requires Category 1 PPE.
    Is there a way to justify using Category 0 PPE - not requiring the use of a face shield?
  2. ctsmiths New Member

    Are you doing voltage tests at the I/O mod or at the transformer? If at the I/O, maybe fuse the secondary side of transformer to lower the AF after the transformer?
  3. haze10 Well-Known Member

    The exception says that transformers under 240V and 125KVA are exempt from analysis. That is because it is unlikely to have a sustained arced at this low a voltage. You just need to be in non-melting PPE, or level -1 to service.
  4. Zog Well-Known Member

    There is no longer a HRC -1.
  5. psThomas New Member

    To clarify my previous post.
    We have a 25kVA transformer (480 to 120/240) feeding a lighting panel. A 20A single pole breaker will then feed a junction box where the 120v is distributed to multiple I/O. Now each individual I/O has a 2A or 1A fuse that will feed the field device (such as solenoid valves, limit switches etc.)

    I feel comfortable considering the load side of the fuses as a Category 0, but am not sure how to regard the line side of the fuses. The table in 130.7(C)(9) for panelboards rated 240V and below would seem to indicate a Category 1 PPE for troubleshooting. But...we have done an arc flash study at our facility and do not know how to deal with incident energy calcs with single phase.

    My ultimate goal is to justify calling the junction box (that is fed by a 20A single pole breaker) a Hazard Category 0 so that we do not need to wear a face shield to troubleshoot.
  6. Zog Well-Known Member

    I think you can safely make that assumption.
  7. psThomas New Member

    Zog,
    I agree with your opinion. But I was hoping for some fact(s) that would back up the assumption. Or do I ask for too much? :)
    I am new to all of this but it does seem that calculations for single phase is non-existant. The only info I have for this case is the table.
  8. WDeanN Well-Known Member

    If you have the study available, put the load in as a 208V three phase behind the transformer, with the breakers in question. You will probably be pleasantly surprised by the results.
    The 3 phase case should be worse case, so your actual energy levels should be even lower.
  9. psThomas New Member

    That sounds like a reasonable approach to assume 3 phase with a 3 phase bolted fault.
  10. WDeanN Well-Known Member

    Just for kicks, I input a 25kVA 208V Xfmr with typical impedence into my software (SKM) and connected it directly to my main 161kV bus.
    After clearing out the exception for <240V (which defaults to Cat 0 if less than 10KA bolted fault or < 125 kVA Xfmr), and giving it a 2 second clearing time, I ended up with 5.1 cal/cm.

    Since you will also have other impedences and shorter clearing times, your values should be much less. I think Cat 0 would be reasonable, judging from this test case.

    Actually, this raises the point that assuming Cat 0 for this case is endorsed by the IEEE 1584 and NFPA 70E if less than 240V, less than 125kVA Xfmr fed, or less than 10kV bolted fault current.
  11. Zog Well-Known Member

    Interesting, thanks. The point is for these low energy system is that the IEEE 1584 group assumes that an arc will not be self sustaining (Like unplugging a hair dryer while running) and the clearing time is irrevelant. However, I have discussed this with people that have done a lot of arc flash testing that disagree with IEEE's assumption. Until we get some good single phase calculations (Is being developed now) we will have to go with the HRC 0 for the exception being discussed here.
  12. Wilson99 New Member

    Is there still a less than 10kA fault current exclusion? I thought the exclusion was just 240V or lower tnf less than 125kVA?
  13. Zog Well-Known Member


    You are correct.
  14. A King Member

    EasyPower under 240V <125kVA Options?

    Does anyone know of such a option for this exception (circuits under 240V fed from <125kVA xfmr) with EasyPower software?
  15. A King Member

    EasyPower: under 240V <125kVA exception option?

    Does anyone know of an option for this exception (under 240V, <125kVA xfmr) in EasyPower software?
  16. haze10 Well-Known Member

    I don't know the internal of EasyPower but I have had some conversations with Chet Davis the owner, and he is always willing to help. Just email him and ask:
    chet@easypower.com
  17. viper57 Member

    Limit Arc Duration

    I use EasyPower and overcome this issue by limiting the maximum arc duration for circuits <240 volts to .167 seconds. This .167 seconds comes from PG&E's arc flash studies whereby the longest sustained arc they produced at 240 volts was .167 seconds. The longest duration at 480 volts was 1.67 seconds.
  18. Mike Frain Administrator

    That is extremely interesting, I understood that faults on 400 volts (here in the UK) could sustain for much longer periods. Have you any links to the research? Many thanks, Mike
  19. brainfiller Administrator

    I would be careful about using the PG&E data for a study. I posted it on ArcFlashForum a while ago and copied it again below:

    PG & E Tests

    This was one company's test results but arc sustainability is quite dependent on voltage, bus spacing, bus orientation, phase barriers and many other things. Right now the only cut off number that is in a standard is 2 seconds which is not a sustainability number but an escape / reaction time number.

    The video below that I received many years ago was from a Portland, OR news crew. It shows a sustained (I believe 480V) fault fed by pole top transformers.

    Sustained Fault

    I wish I could give you a better cut off value but for now, there is still too much that we just don't know about yet.
  20. StinnettW New Member

    Does 70E explicitly say you can assume Cat 0 under 130.3 Exception No. 1? I see that it says an arc flash hazard analysis is not required, but I can't find where Cat 0 is implied. The alternative is that you have to use table 130.7(C)(9) which does show examples of Cat 1 Hazard when performing tasks such as voltage testing.