1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Meters and Incident Energy

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by brainfiller, Jan 10, 2009.

  1. brainfiller Administrator

    THIS IS FOR INFORMATION ONLY - DO NOT BASE STUDIES ON THIS DATA - IT IS JUST ONE COMPANY'S TESTS!! (<<had to put the legal thing in here)

    Hi Everyone,
    There has been quite a bit of discussion and debate about what to do when working around meter bases. At one of the IEEE 1584 meetings, a presentation was made about arc flash testing on 480 V meters.

    The problem is there is usually no protection directly upstream from the meter. Using IEEE 1584 formulas you can get some pretty huge incident energy numbers.

    One of the committee members that works for a large electric utility questioned the large numbers from the calculations. The thought was they don't have much data to support lots of people being injured or killed while working on meters when an arc flash occurs.

    They decided to conduct their own testing and here is what they learned (again take note of the legal thing at the top - this is just FYI info)

    They tested both self contained meters and transformer (CT) rated meters at 4 different fault current levels.

    6.6 kA
    12.7 kA
    25.7 kA
    44 kA

    480 Volts
    18 inch working distance (where calorimeters were located)

    The results were surprising.

    Self Contained Meters:

    10 tests at each current level for a total of 40 tests.
    Maximum measured incident energy was 21.1 cal/cm2
    Each test was above 4 cal / cm2
    15 were above 8 cal/cm2 (less than half of the 40 tests)

    CT Rated Meters

    46 total tests.

    Max measured incident energy was 10.7 cal/cm2
    All but one was BELOW 4 cal/cm2

    The duration was the big thing. The arc extinguished usually due to the bus vaporizing. Higher current often produced faster extinction (quicker vaporizing of conductors)

    What does all this tell us?

    IMHO - great info but we still have a lot more to learn.
  2. wbd Well-Known Member

    Jim,

    Thanks for providing the information.