1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

HV Fuse operating fault on LV Side

Discussion in 'General Discussion' started by varun.singhal, Jan 10, 2009.

  1. varun.singhal New Member

    I am doing an arc flash assessment and have came across a strange observation. Wanted to get some confirmation from others experience....

    I have a LV system (0.415kV) fed by transformer (3.3/0.415 kV) protected by a 250A HRC fuse (GE K81 PEX) for shortcircuit on HV feeder. For a fault level on 0.415V LV side (~19kA 100ms symmetrical rms), the fault current seen by fuse on HV is around 2kA. As per the pre-arcing time vs. prospective current graph of fuse, it will melt in 4s. This gives a hazard category of X

    My take on the observation is: Fault current on LV is much less than the switchgear rating (63kA), which when reflected on primary would be even less ..... hence fuse take more time to trip this giving high hazard category.

    Want to confirm I am not doing anything wrong. And such observations with LV are usual???
  2. John Perrotti Member

    Energy & Time

    You have just understood the relationship to the release of energy, and the time it takes to clear it.

    Higher categories can be achieved at lower current levels when the time it takes to clear is excessive. Just like the sun, you can get a second degree burn if you are exposed too long.
  3. Zog Well-Known Member

    Yes this is a typical problem for industrial plants, can be mitigated but not easy to do and expensive.
  4. McFlash New Member

    There is always the 2 second rule in the IEEE 1584. If you use this as a cut off time it may offer lower IE.