1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Help with calculation

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by H2Os, Jan 2, 2009.

  1. H2Os New Member

    :confused:I have been trying to figure out if I am doing this right before I continue on. I pick one machine that is hook up to a 480v bus that is feed by a Pow-R-Way switchboard, It is feed by 2500kva transformer. There is no fuses or CB between the transformer and switchboard.

    Attached Files:

  2. acobb Well-Known Member

    Help

    I think that before anyone here can help, you must supply more info and actually ask a question.
  3. haze10 Well-Known Member

    also give impedance of transformer, cable type and lengths, and if the panel is MLO or MCB.
  4. H2Os New Member

    Sorry my zip attachment was missing. There is a line drawing in a PDF format plus a word doc that has my questions.
  5. WDeanN Well-Known Member

    I haven't looked much into the rest of your calculations, but I question the 0.1 sec clearing time on bus one. If this is based on the fuse upstream of the main transformer, then the clearing time is likely to be much longer.
  6. H2Os New Member

    Yes you are right the clearing time should be higher. I still cannot get any information from the utility company. So I just used 0.1 sec to start with.
  7. haze10 Well-Known Member

    Where are you getting your PPE Levels.
    At the main bus you show an IE of 5.6 cals and a Class PPE of 1.
    If Class is the same as Level, then it should be Level 2, (4-8 cals).
    For IE under 4 cals you are showing Class 0. These should be Level 1.

    Are you trying to indicate the NFPA PPE Level or something else.
  8. H2Os New Member

    Did they remove the hazard/Risk category 0 in NFPA 70E 2009. I was try to find any information on this change in category.
  9. wbd Well-Known Member

    Category 0 is still in Table 130.7(C)(11) in NFPA 70E-2009 and this would be applicable up to 1.2 cal/cm2. Above 1.2 cal/cm2, FR clothing is required as per Article 130.7(C)(5).

    IMHO, I think Table 130.7(C)(11) should have 5 J/cm2 (1.2 cal/cm2) in the Required Minimum Arc Rating of PPE column, not N/A for Category 0. This would make the table consistent with the text in Article 130.7(C)(5).
  10. H2Os New Member

    I change the Category levels, I must have miss read or type them in wrong
  11. tylerbliss New Member

    Calculating Bolted Fault Current

    I need some guidance on calculating BOLTED FAULT CURRENT.
    I cannot find out how to get access to IEEE-1584 which I would assume would answer most or all of my questions. I would appreciate advice from anyone wiser than I.
    Here is what I have assumed (please correct me where I am wrong).

    I = E/R.
    I = Bolted Fault Current
    E = 460vac (in my case) but I have questions below.
    R = ‘the big mystery’

    I assume that R = the aggregate impedance (@60hz) of the following:

    1. Secondary of my transformer.
    2. Wiring impedance all the way to the flash point (as found by using info from my ‘Ugly’s’ book pg 66.)
    3. Safety factors & K factors which I hope a wise person can inform me of.

    Questions:
    1. When figuring wiring impedance, do I use ‘distance to flash point’ + ‘distance back from flash point’ at 460vac OR ‘distance to flash point’ only @ 277vac OR some other method?
    2. What are ‘standard safety factors’ and K factors commonly accepted (if any)?

    A phone call would be welcomed as well.
    417-208-1352
    Tyler Bliss

    Thanks
  12. haze10 Well-Known Member

    Calculating fault currents isn't difficult but it takes some industry understanding of what the numbers all mean.

    Go to your transformer nameplate and find out the Impedance %, it should say something like 5.75%.

    Contact your utility and ask for Fault MVA and X/R ration to your transformer.

    Identify the type of cable from the transformer secondary to the point of the potential flash location under review. If you are going through multiple gear identify type and distance for each run, and type of raceway. You just need to list for one phase, the other phases are identical. So for example, from transformer to switchboard, 4 parallel 500 MCM copper in EMT x 80 ft. From switchboard to lighting panel (point of flash) 1 each 4/0 Copper in tray cable x 300 feet.

    Estimate the total KVA motor load and identifier any synchronous motor or generators.

    I take it you don't have software, and you don't need it for small sites. Most of us would probably do this with the 'per unit' method of calculation. But it sounds as if you might need something easier to start with. For arc flash calcs, which only looks at 3 phase bolted fault, I like the MVA method for calculating faults. It follows the V=IR type of equations you seem to prefer.

    Go to arcadvisor.com and investigate the method. If you don't find it, contact the owner and ask him for the white paper on the MVA method. If you have a limited number of points, spend the $50 and sign up with him and use his on line software. But let me warn you its a bit quirky until you understand how to use it.

    In the back of your NEC book find the table for Conductor Properties, look for the Z impedance values for you cables and type of raceway.

    Report back with more info.