1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Testing of Circuit Spout on ABB Internal Arc Proof Switchgear

Discussion in 'Equipment to Reduce Arc Flash Dangers' started by varun.singhal, Dec 23, 2008.

  1. varun.singhal New Member

    Here I am referring to a particular MV SWGR from ABB Unigear type ZS1 (http://www.abb.com/product/db0003db...690029a3e2.aspx?productLanguage=us&country=00) which is internal arc proof as per catalogue.
    Just to make it clear: The switchgear has three separate segregated sections one each for bus, breaker and circuit.

    I have one particular operation where prior to earthing the circuit (done with doors closed), I will have to test the circuit spouts with appropriate tester for proving it dead (Working distance ~ 1000mm). Before opening the circuit section door for testing (lowest one), I would have opened the breaker (middle section) and isolated it as well. Would there still by any arc flash hazard while testing of circuit spouts now? If yes, can you explain me how?

    Thanks
  2. jghrist Well-Known Member

    If there is no possibility of the circuit spouts being energized, why is there a need to test them?

    If there is a possibility of them being energized, then there is a possibility of an arc.
  3. haze10 Well-Known Member

    Rule of thumb is the circuit is NOT safe until the grounds are on. Testing voltage for verification that the circuit is open, is subject to full PPE requirements. You test to verify something didn't fail, like one leg staying closed. After grounds are on, no electrical PPE is required.