1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

How would you label this?

Discussion in 'Arc Flash Labels' started by Pghwireman, Dec 19, 2008.

  1. Pghwireman New Member

    This system consists of a 5KV feeder to a load break disconnect ahead of a 1500KVA (4160/480) xfmr to a main breaker. Calculations were made using the SKM software & the IEEE standard.

    The rating of the main breaker line side(81) is calculated at a Dangerous category. The load side bus is calculated at a Category 3 rating. The feeder breakers off of this bus are rated Category 2 & one device is rated as a Dangerous category. The substation bus is contained with in barriers within the gear. Removing the rear covers exposes only the load side terminals of the breakers.

    The normal tasks performed in this facility are typically rear cover removal for IR scanning, voltage & amperage tests. The entire system follows a stringent PM cycle at which time the substation is de-energized and the breakers are tested & calibrated. Due to the high incident energy of device 83 as well as other locations with in the facility the customer has ordered a remote racking sled in case the breakers needs to be racked out when the sub is energized.

    How would you label this, specifically Sub 5? I think this could play out a few ways.
    Do you label all breaker cubicles at a HRC 3 level since they are connected to the bus? Would you label the rear covers with the HRC 2 level since that is all that is exposed (load side of breakers) when the covers are removed?

    Your thoughts?

    Attached Files:

  2. Zog Well-Known Member

    I am confused about your 82.5 cal/cm2 on device #83. 82-89 should all be about the same


    Where do you get HRC 3 from? Having different labels on the front and back is fairly common. Have you considered mitigating these? Easy fix for sub 5 (Besides the main) is retrofit the main with a trip unit that has arc flash reduction capability. We do those every day. The main breaker and the transition section on the 480V side of the transformer is tougher but I have mitigated that down to HRC 1 at a few plants.

    Sounds like they have the racking figured out, what about operating the breaker before racking? Have a solution for that one yet?
  3. Gary B Well-Known Member

    Since you cannot control who will have access or how they will interpret the labels, I would label the entire lineup as Dangerous since that is the exposure available on the line side of the main breaker. This makes a compelling case for detached main breaker located on the transformer secondary.

    It is debateable whether to label the rear access panels at the lower Risk Category 2 IF that is the only exposure there, and it is very obvious the reduced hazard is only for those compartments with higher risk category labels on the front compartments.