1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Article 130.3 Exception No. 1

Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by wbd, Dec 3, 2008.

  1. wbd Well-Known Member

    Exception No. 1 (2) states that one of the conditions where an arc flash hazard analysis is not required is where the circuit is fed by one transformer.

    This question may be nit picky or reading too much into that statement but in mind when I see that one transformer is mentioned, I think of a 3 phase single transformer. However, I have seen many facilities fed by an overhead service from the utilities 3 phase transformer bank consisting of 3 single phase transformers.

    Does a 3 phase transformer bank, consisting of 3 single phase transformers, meet Exception No. 1 (2) of one transformer?
  2. acobb Well-Known Member

    Three single phase transformers in a bank have the same electrical characteristics as 1 - 3 phase transformer of equal size.

    ex...3-100 kVA single phase transformers = 1-300 kVA three phase transformer.

    I believe it only applies to 240 volts or less and <125 kVA.

    Alan
  3. WDeanN Well-Known Member

    Exception No. 1: An arc flash hazard analysis shall not be required where ALL of the following conditions exist:
    (1)
    (2)
    (3)

    ALL of the conditions listed must exist.