1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

How Many Arc Flash Labels on Switchgear?

Discussion in 'Electrical Safety Practices' started by LHall, Nov 11, 2008.

  1. LHall New Member

    Hi everyone. Need a few opinions about labeling switchgear. We are thinking of labeling the two mains separately since their incident energy is dependent on the upstream device. We would have a label for each distribution section based on the setting of the 2 mains. We are thinking of putting labels on the back but this might be overkill. Does this make sense?

    The tie is causing us to question ourselves. If someone is working in this area live with the tie racked out, removed or open and the 2 mains closed (normal condition for us), won't the fault current be coming from both mains and meet in the middle for a much larger fault current if something really rare happens? This is probably a very very remote chance but it seems everyone is playing (overly?) safe.

    Thanks!
  2. haze10 Well-Known Member

    I can't speak to the specifics of your site but will offer a general opinion.

    1) If at all possible rate the whole switchgear lineup to the same rating. This allows for the least complexity. If you can do this, I would put the labels at the top of each section and one on each back door.

    2) If #1 is not possible then do as you indicate. I would probably then put labels on each cubicle. I think that an average person may walk up to the gear, read one label and assume it is for the lineup. So you need more labelling under this condition, and it also needs to be covered in training that switchgear may have multiple ratings.

    3) As for the multiple source tie. If the tie is normally closed, then you need to include both sources in the analysis. If you haven't, then I assume its because having the tie closed is not normal. You need to cover this special condition in your training, and make it an exception to routine work that requires a permit. You should analize that condition and know what the new IE is for that condition. You can also put on your label next to the IE value 'Tie Open' or some seperate label. If the condition is restricted to just your employees and they are trained to the condition, I wouldn't say more labelling was a must do.

    Multiple conditions are tricky. Best is to design for the worse case if possible, but it not possible, then it has to be covered in training or added labelling.