1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

NESC Table 410-2: Determining Arc Gaps

Discussion in 'NESC - ANSI C2 - National Electrical Safety Code' started by Electric John, Sep 18, 2008.

  1. Electric John New Member

    Hi,

    in the NESC-2007, at the bottom of Table 410-2, it states that

    Arc gap—calculated by using the phase-to-ground voltage of the circuit and dividing by 10. The dielectric strength of air is taken at 10 kV per inch. See IEEE Std 4-1995.

    I have the Standard IEEE Std 4-1995. In chapter 17, I see some documentation about gaps. I'm sure not sure what section is used to determine those arc gaps for Arc Flash calculation.

    Has anyone search for default arc gap for transmission voltage? I'm not sure I understand the calculation.

    When reading the footnote, I wondering, does it literally means that:

    Arc gap = Vlg / 10

    example: 69 kV L-L
    Arc gap in inch = 69 / sqrt(3) / 10 = 4 inch?

    Doesn't look right.

    Thanks
  2. RobGOlson New Member

    I have the same question.

    For a 345 kV bus, is the arc gap = 345/1.73/10 = 19.9 in ?

    If anyone has an answer for this it would be greatly appreciated.
  3. jghrist Well-Known Member

    I believe you are correct. The assumption is that the gap will be the distance that would breakdown at the Ø-grd voltage. 199 kV / 10 kV/in = 19.9 in. I used this assumption with ARCPRO to get the max clearing time value given in Table 410-2.
  4. stevenal Well-Known Member

    Don't forget that the table was changed via a TIA. The new tabulated results can be verified with ArcPro, the original ones could not.
  5. jghrist Well-Known Member

    The new one is the one I verified.
  6. Michael Furtak New Member

    69kV line 4 inches apart ???

    Have anybody seen 69kV overhead lines 4 inches ( 10cm ) apart ??? Or 345kV lines separated by 19.9 inch ( 0.5 meter ) gap? I don't believe 10kV / inch dielectric strength for air value is practical. It might probably apply to dry, still air without contaminants, even electrical field etc. The practical dielectric strength would be a fraction of the intrinsic dielectric strength seen for ideal, defect free, material. I remember 1kV / cm rule of thumb from school. Could anybody please provide with a copy of IEEE std 4 page proving the 10kV per inch value?
  7. acobb Well-Known Member

    The arc gap has nothing to do with the phase spacing of the line. It is the "assumed" gap for the purpose of calculating the IE associated with a line to ground arcing fault. After all if there was no gap, there would be no arc.
    ________
    Water Bong
  8. arcad New Member

    I have similar question regarding arcing gap in new CSA Z462 standard article D.8 derived from NESC tables 410-1 and 410-2. For visualization purposes, check a plot displaying arc gap as a function of system voltage - all according to the tables 410-1 and 410-2 from NESC or tables D.6 and D.7 from CSA Z462

    [IMG]

    The jump at 46kV point is most obvious and alarming. The problem with the 10kV/in number and arc gap calculated based on it is that it is used in calculation the distance from the arc to the worker, namely CSA Z462 Table D.7 Note 2 states the distance from the arc to the worker is calculated using the minimum approach distance from Table 441-2 of IEEE C2 and subtracting two times the assumed arc gap.

    Any comments?
  9. acobb Well-Known Member

    Since I have not had a need to use an arc gap above 35 kV so far, I have never checked to see what a gap for 46+ kV would be. Sure seems to be a dis-continuity in the arc gap calcs as you have noted. This should probably be submitted to the committee for consideration during the comment period.
    ________
    ExoticPetite live
  10. arcad New Member

    Thanks, Alan. I will escalate this issue to the CSA Z462 powers.

    - Michael
  11. stevenal Well-Known Member

    Arcad,

    The unstated assumption in table 1 (as I've understood it) is that rubber gloving is used. Table 2 says it is for live line tool use. Not sure it explains the discontinuity, but it is an important difference.
  12. jghrist Well-Known Member

    ARCPRO result with Table 410-1, 9" gap and 15" clearance, 30 kA, 30 cycles, 26.6 kV = 63.8 cal/cm²

    ARCPRO result with Table 410-2, 2.66" gap and 15" clearance, 30 kA, 30 cycles, 26.6 kV = 37.9 cal/cm²

    ARCPRO result with Table 410-2, 2.66" gap and 2'-3.68" (2'-9" minus 2 times gap) clearance, 30 kA, 30 cycles, 26.6 kV = 11.2 cal/cm²
  13. arcad New Member

    Could anybody having an access to ARCPRO please provide the ARCPRO incident energy results for:

    1) 9" gap and 15" work distance, 20 kA, 60 cycles ( 1 sec ), 46 kV

    2) 2.7" gap and 33" work distance, 20 kA, 60 cycles ( 1 sec ), 46.1 kV

    3) 9" gap and 20" work distance, 20 kA, 60 cycles ( 1 sec ), 46.1 kV

    Thanks

    M. Furtak
  14. stevenal Well-Known Member

    78.7, 8.6, 45.1 cal/cm^2

    with copper electrodes. Note that the distance in Arcpro is not a working distance to conductors, but distance to the arc.
  15. arcad New Member

    thanks stevenal. I thought the
    energy would equal to 12.4 cal/cm^2 based on Table 441-2. What you say Arcpro produces even smaller number ( 8.6cal ). Do you know how to explain almost 10X reduction in incident energy from 78.7cal/cm^2 to 8.6cal/cm^2 for 46kV 20kA 1 sec duration arc when moving 18" = 33" - 15" further away from the arc? I would expect factor of 4X when working distance was doubled but ten (10X) times reduction in incident energy is somehow hard to believe. Could you please let me know what I am missing here?
  16. jghrist Well-Known Member

    Table 410-2 has a range of voltages from 46.1 to 72.5, with the results shown for the highest voltage.

    The arc gap makes a large difference also. The 33" working distance with a 9 inch gap would give 16.8 cal/cm², closer to 1/4 of 78.7.