1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

PPE on Dead Bus

Discussion in 'Personal Protective Equipment (PPE)' started by hydropwrbb, Sep 17, 2008.

  1. hydropwrbb New Member

    On a 13.8 KV switchgear that is a level 4 rating. If the bus voltage was deenergized through switching and verified with open breakers, would there still need to be AF level 4 clothing worn to rack out the 13.8 KV breaker?
  2. Zog Well-Known Member

    Yes, until you have done a voltage (live-dead-live) test and applied protective grounds 13.8kV switchgear is still treated as energized. See Article 120 in NFPA 70E or OSHA 1910.269.

    Another alternative is to rack the breaker from outside the arc flash boundary
    www.remoterackingsolutions.com
  3. hydropwrbb New Member

    Thanks very much. I had reviewed Art. 210 but met some opposition from craft on level of exposure. If I understand it right, until we are grounded after verification of being dead, we use the same level of protection that would be required as if it was live.
  4. Zog Well-Known Member

    You are correct, and you should be wearing the same PPE to verify it is dead and to install grounds.

    I know, I know, chances are about 99% that it is dead when the breakers are open, but I have seen that other 1% happen, there are several things that can go wrong and ot still be energized. It only takes 1 time,

    If your crew needs some convincing, get "The Mark Standifer story" , arc flash victim on 13.8kV, 13.8kV switch, 1 phase didnt open, he didnt check it dead and nearly died because of that failed phase on the switch that didnt open, you can get it from ERI safety videos.
  5. geh7752 Member

    I've also seen situations where a bus being back fed from another source due to a defective tie breaker. Always test before you touch....