1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Cable Limiters

Discussion in 'General Discussion' started by blackdog, Sep 9, 2008.

  1. blackdog New Member

    Can cable limiters be used to reduce the fault current levels and thus allow for smaller KAIC rated circuit breakers?
  2. brainfiller Administrator

    This would fall under NEC 240.86 Series Ratings which allows both tested combinations of devices for series ratings as well as series ratings under engineering supervision in existing installations (with specific provisons).

    Series ratings - what you are asking about - have an odd history. I was involved with a bit of the history way back when I was at Square D in the early 1980's. At one time, series ratings were determined by fuse let thru curves. This generally worked out but a bit of controversy errupted about the application methods (I won't go into it here but it was quite an interesting time). Eventually let thru curves were not used as much but actual tested combinations of devices were used instead (combinations were listed in tables created by the manufacturers) These tested combinations were developed in conjuction with Underwriter Laboratories.

    Requiring all series ratings to be tested combinations later lead to a question/problem with older installations where series ratings were needed but the older equipment was never part of the testing program (Like your case??) Because of this problem with older/existing equipment and series ratings, the NEC was revised to allow the use of series ratings of components "selected under engineering supervision"

    So the long answer to your short question is yes it is possible that the limiters could protect dowstream breakers but someone (a licensed Professional Engineer according the the NEC) will have to perform an analysis to determine if it would work and then (here comes the hard part....) the P.E. must sign off and stamp it.
    a.k.a. liability issue. :eek:

    However, not knowing who you work for, cable limiters are often used in electric utility underground networks. - Utility transmission and distribution systems are exempt from the NEC NEC 90.1(B)(5)
  3. blackdog New Member

    Thanks, Jim.