IEEE-1584 Bolted Fault Current Spreadsheet
Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by sharonkr, Sep 5, 2008.
  1. sharonkr New Member
    Has anyone any experience in using this spreadsheet?
    I tried calculating the bolted fault current using this spreadsheet but my results were very different from using another software. Eg, I got around 6kA as my bolted fault level using this spreadsheet and 2.97kA using a fault calculation software.
    Help please.
  2. Homerjs78 New Member
    Thats a pretty big difference. Can you provide an image showing the two side by side?
      File size:
      95.1 KB
      112
      File size:
      32.3 KB
      56
  3. acobb Well-Known Member
    Are you using the same transformer %Z and source %Z in both cases and are both giving you 3 phase fault values? Same x/r ratio?
    Alan
  4. brainfiller Administrator
    I have used the IEEE calculator before. It works but there are many little things lurking around that can give you the wrong answer and you may never know it. I was solving a problem last week in a class by hand and someone asked me to try it with the IEEE calculator. I dropped in the numbers and got the wrong answer. I only knew it was wrong because I had solved the problem before. After sifting through all of the various factors including looking at the log (Ia) etc. I saw where it was going wrong. As you gain experience and confidence with the calculator it works well but if people just jump into it.... the old saying "Garbage in Garbage out" still applies. Good Luck with it!
  5. CMWilson New Member
    I have used the IEEE spreadsheet calculator also. It works but you really need to be careful that the set up is correct - gap - box etc. If you can spring for one of the commercial programs like SKM or EasyPower, it goes much better - but of course it costs $$$
  6. sharonkr New Member
    Thanks guys.
    Please refer to the attachment. This should be a fairly simple as I want to know the fault level after the generator (I have no even reached the tranformer stage)! I must be inputting something wrongly in the IEEE calculator but I just can't seem to find it.
  7. jghrist Well-Known Member
    The "Available MVA" in the IEEE calculator is not the generator rating. It is the available fault MVA. If you are going to use a generator as the source, then divide the rated MVA by the per unit subtransient reactance to get the fault MVA.
  8. sharonkr New Member
    Thanks for the advice! It really helped!
  9. Yuna New Member
    i fail to get the IEEE 1584 excel sheet. Does anyone can send it to me? Really thanks for your kindness.
    Yuna
  10. jghrist Well-Known Member
    If you purchased the IEEE 1584 standard, you should have gotten the spreadsheet with it. If not, contact IEEE with your invoice information and they will help out.
  11. arcad New Member
    check AFA v3.0 The program is based on IEEE 1584 same as the original IEEE spreadsheet and also allows to calculate initial pressure generated by arc blast and arc flash explosive TNT equivalent.