1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Please support this Proposal

Discussion in 'NFPA 70 - National Electrical Code - NEC (R)' started by JoeTedesco, Aug 30, 2008.

  1. JoeTedesco New Member

    NFPA ACCEPTS PROPOSALS ONLINE

    Log Number: 586 Section/Paragraph: 110.16 - Proposal for the 2011 NEC

    Submitter: Joe Tedesco, Boston, MA

    Recommendation: Delete the following words: "that are in other than dwelling occupancies," so that the text in the 2011
    NEC will read as follows:

    110.16 Flash Protection.

    Electrical equipment, such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor
    control centers, that are likely to require examination, adjustment, servicing, or maintenance while energized shall be
    field marked to warn qualified persons of potential electric arc flash hazards. The marking shall be located so as to be
    clearly visible to qualified persons before examination, adjustment, servicing, or maintenance of the equipment.

    Substantiation: I live in a nine story building that is supplied by a 1000 amp, 208Y/120 volt, 3 phase 4 wire service, that
    includes electrical switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control
    centers, that often require examination, adjustment, servicing, or maintenance while energized.

    Each dwelling unit is supplied by a 125 amp feeder, and has a panelboard installed in a clothes closet.

    The building was built before the code added the rule in 240.24(D).
    Adding a field marking to warn qualified persons of potential electric arc flash hazards where it will be clearly visible to
    qualified persons before examination, adjustment, servicing, or maintenance of the equipment will enhance safety.

    See this video and audio of the equipment room in my building:

    http://www.youtube.com/watch?v=HKjAmaH6xxk#
  2. K. Jackson New Member

    I understand the concern with your building's large service but isn't this over reaching into single family dwellings with small individual services? Perhaps some language about this applying to a service above a certain size like maybe 600 Amps? << just randomly picked that number, some thought could be put into what is a good size service. Maybe make it not applicible to residental services below some number. Maybe it just applies to multi tenent dwellings. I would hate to see the burdon continue to grow and reach into my house's 200 A panel fed from a very small transformer. There seems to be a lot of discussion in this forum about over reaching and the huge burdon resulting from all the new rules.
  3. JoeTedesco New Member

    Here's what the CMP said for the first proposal I sent

    1-82 Log #1651 NEC-P01 Final Action: Accept in Principle
    (110.16)
    _____________________________________________________________
    Submitter: Joe Tedesco, Boston, MA
    Recommendation: Revise text to read as follows:

    110.16 Flash Protection. Switchboards, panelboards, industrial control panels,
    meter socket enclosures, and motor control centers and are likely to require
    examination, adjustment, servicing, or maintenance while energized shall be
    field marked to warn qualified persons of potential electric arc flash hazards.
    The marking shall be located so as to be clearly visible to qualified persons
    before examination, adjustment, servicing, or maintenance of the equipment.

    Substantiation: Removing the words: “that are in other than dwelling
    occupancies†makes sense because the hazards exist dwelling occupancies too.

    Many dwellings have services that are 400 amperes or more, and some
    services are located within commercial occupancies where there are stores and
    dwelling units all served by the same electrical utility system. I believe that this
    change will be in the best interest of safety. With the warning sign present a
    qualified person who may be a Home Inspector or NACHI member will be
    aware of the need for some form of PPE, probably Catagory 2.

    Panel Meeting Action: Accept in Principle
    Revise text to read as follows:

    110.16 Flash Protection. Switchboards, panelboards, industrial control panels,
    meter socket enclosures, and motor control centers that are in other than one and
    two-family dwelling occupancies and are likely to require examination,
    adjustment, servicing, or maintenance while energized shall be field marked to
    warn qualified persons of potential electric arc flash hazards. The marking shall
    be located so as to be clearly visible to qualified persons before examination,
    adjustment, servicing, or maintenance of the equipment.
    Panel Statement: The panel has revised the proposal to only include one- and
    two-family dwelling occupancies rather than all dwelling occupancies because
    one- and two-family dwellings provide a reasonable demarcation for
    occupancies where arc flash hazards may exist. The panel does not necessarily
    agree with all of the substantiation of the submitter.

    Number Eligible to Vote: 12

    Ballot Results: Affirmative: 8 Negative: 3 Abstain: 1

    Explanation of Negative:

    LABRAKE, JR., N.: This proposal should be rejected. Qualified persons
    understand that equipment is to be placed in an electrically safe work condition
    before maintenance is performed. Generally, this can be readily accomplished
    in dwellings. Unlike some instances in commercial and industrial installations,
    it is not likely that electrical equipment in dwellings typically operated at less
    than 300 volts would have to be maintained while energized, and, therefore, do
    not need to be marked as to arc flash hazards.

    MCMAHILL, L.: Although I agree that arc flash hazard exists in dwelling
    occupancies, I disagree that it exists at the same level as in other than dwelling
    occupancies. Panelboards and meter sockets in dwelling occupancies are not
    subject to the same scrutiny as commercial and industrial type occupancies,
    and the potential arc flash energy is generally less too. Expanding the marking
    requirement to include dwellings other than one- and two-family is excessive.
    The marking requirement will apply to all panelboards and meter sockets in
    multi-family dwellings. This is over restrictive and provides no useful purpose.
    Flash protection warnings are intended for “qualified persons†working on
    energized equipment, such as in commercial and industrial type facilities.
    Adding such marking on dwelling equipment appears to only encourage
    working on equipment while energized. Equipment in dwelling occupancies
    should always be deenergized before servicing!

    MINICK: NEMA continues to support the position that personnel safety can
    best be assured when equipment is de-energized before performing any work.
    Explanation of Abstention:

    Explanation of Abstention:

    FISKE, W.: We are abstaining from voting on Proposals 1-82, 1-83, 1-84, and
    1-85, as they relate to field marking of arc flash hazards. There is no role for
    conformity assessment bodies (i.e., nationally recognized testing laboratories)
    to play in fulfilling the existing or proposed requirements. As we are not an
    affected party, Intertek has elected not to take a formal position on the four
    proposals identified above.