1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Electrically Safe Work Condition

Discussion in 'NFPA 70E - Standard for Electrical Safety in the W' started by GPD_Steve, Jul 14, 2008.

  1. GPD_Steve New Member

    What is everyone's opining about wearing PPE to visually verify that all blades of a disconnecting device have fully opened or to do voltage testing to verify all phases are deenergized?

    NFPA, Article 120.1 Process of Achieving an Electrically Safe Work Condition describes the procedure to establish and electrically safe work condition. When a worker interrupts the load current by opening a disconnecting device and opens the enclosure they could be exposed to energized parts. Should someone wear PPE while visually inspecting the device and while performing voltage testing?

    I have a client who insists several 480V disconnects throughout his system do not need specific arc flash labels. He states, "devices do not need specific arc flash labels for the testing of voltage to determine if a device is de-energized."

    I do not agree. Any thoughts?
  2. Zog Well-Known Member


    You are correct, your client is not. Until you have established an Electrically Safe Work Condition the equipment should be treated as energized, which means wearing the correct PPE.

    Refer your client to the 70E tables that have the PPE requirements for checking for voltage and application of safety grounds after voltage test, in fact the PPE requirements in the tables is higher for these tasks than other tasks on the same equipment when energized.