1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

85% Arcing Current

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by Brian G., Jul 24, 2007.

  1. Brian G. New Member

    Why do the computer programs use both 100% and 85% arcing current in determining the incident energy?
  2. Catcher13 New Member

    There was a minor revision / enhancement to IEEE 1584 in 2004 that added the 85% At one time the calculations required the input of "bolted" short circuit current data i.e. no arcing impedance that would reduce the amount of current that flows. Then IEEE 1584 developed a method for estimating / calculating the arcing short circuit current based on a number of tests. The significance of the arcing current is so you can look at a time current curve and determine how long it takes an overcurrent device to operate based on the current during the arc flash. After the 2002 1584 was issued, there was concern that "what if" the arcing current was a little lower than estimated. That could make the difference between whether the device operated instantaneously or timed out in the overload region - having a huge effect on the incident energy. Now you evaluate it at 100% and also 85% to see if 85% causes a longer clearing time that would lead to much worse incident energy. The worst case of 100% vs. 85% is used for the final results.
  3. arcflashstudy New Member

    "there was concern that "what if" the arcing current was a little lower than estimated"

    What are the reasons for arcing current to be lower than estimated?
  4. geh7752 Member

    Many factors can change arcing current... lower available ultility fault currents, voltage fluxuations, cable impedance and cable run distance, etc.
  5. acobb Well-Known Member

    By its definition, an arcing fault is not a bolted fault, and the arc has resistance as well.
  6. ekalbs4 New Member

    My interpretation of the 1584 amendment is that the 85% arcing current calculation is only intended for use on <1kV and that when performing calculations >1kV, 100% should be used.
  7. brainfiller Administrator

    That is the general concensus for the interpretation. Above 1 kV values of Ibolted and Iarcing begin to converge with only a small difference between the two. I believe most (all?) software also use this interpretation.
  8. ekalbs4 New Member

    In case it may help someone else, I'll note that at least one software is having some trouble with applying the 85% correctly based on voltage.

    The SynerGEE software v3.8.3.153 by GL (formerly Advantica) calculates arcing current at both 85% and 100%, but the summary report only displays the resulting incident energy that is greatest, so it could be from the 85% or 100% value, which is okay for <1kV, but not expected for >1kV. There is a separate report to see the details, the problem is with the summary report.

    Another problem is that the software appears to have an option to modify the reduced arcing current from 85% to any specified value, but this setting does not actually do anything at this time. You would think that you could force the calcs to 100% using this setting when studying >1kV, but it currently does nothing.
  9. JayWes38 New Member

    By definition an accident is undefined; one does not know the length of the arc, its plasma content; therefore what the true arc current will be is also unknown. There was a paper given at NFPA in Boston in which an engineer discussed the problem of a generator when the Arcing current was low enough that it resulted in a long time to clear resulting in very high heat releases.