1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

what PPE needed question?

Discussion in 'Personal Protective Equipment (PPE)' started by Justa_Sparky, Jun 14, 2008.

  1. Justa_Sparky New Member

    The more I read the more confused I get.

    Okay here is an example I am troubleshooting an e-stop circuit in a two bay panel. On the disconnect bay of the panel is all the 480 volt motor starters and 480 volt terminals. On the other bay are the plc and 120 volt AC and 24 volt DC control circuits.

    The arc flash study shows the panel as a category 0.
    With an arc flash boundary (AFB) of 5 inches, with a 0.3 cal/cm2 calculation.

    My understanding is to troubleshoot the ac control with a VOM all I need is shock protection (rubber gloves) because I will not be in the AFB. But if I get within 5 inches while troubleshooting of the 480 volts Arc Flash PPE will be needed.

    But what if I am 9 inches from 480 volts operating a selector switch that is mounted in side the panel? Do I need rubber gloves and a long sleeve shirt on?

    Thanks for the help
    Steve
  2. Zog Well-Known Member

    Yes, because you are within the RAB for 480V which is 12"

    All your other assumptions earlier in your post were correct.
  3. Justa_Sparky New Member

    Thanks for the reply

    So a long sleeve shirt is needed for shock hazard not just arc flash?

    Thanks again
    Steve
  4. Zog Well-Known Member

    No, sorry I missed the LS shirt part of your question. Any part of your body (Or conductive object you are holding) that crosses the RAB needs to be insulated for the voltages present.

    The FR (Or natural fiber for HRC 0) clothing is all for Arc Flash protection.